Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Unable to find Custom SmartConnector assembly

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to find Custom SmartConnector assembly
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • MaximeLaudren
    MaximeLaudren
  • CraigEl
    CraigEl
  • David_Kendrick
    David_Kendrick
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2562 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to find Custom SmartConnector assembly

Product_Support
‎2018-09-10 09:42 AM

Last Updated: CraigEl Champion ‎2021-12-21 01:20 PM

Issue

When configuring a SmartConnector, the custom assembly cannot be seen in the Add Processor Configuration tab.

 

Untitled.png

Product Line

EcoStruxure Building Operation

Environment

Microsoft Windows Server 2012 and newer, Windows 10

Cause

Microsoft Windows Server

Unsigned or unknown certificates

Some files need to be "unblocked" after download in order to avoid security warnings from tools like Visual Studio about potentially unsafe content.

 

This is because the dll’s for the custom processor have been downloaded from an internet based source.

 

Otherwise, all the required dll’s for the solution may not be available in the service installation directory (normally “C:\Program Files (x86)\Schneider Electric\SmartConnector”). This information can be seen in the SmartConnector log file. SmartConnector will log an error when going to the point of adding a new processor if it can’t find a reference. It will point to the assembly which is missing.


Microsoft Windows 10

The service needs to be restarted once the dlls for the custom processor have been added in the service installation directory.

(“C:\Program Files (x86)\Schneider Electric\SmartConnector”)

Resolution

Microsoft Windows Server range

To "unblock" a file,

  1. Right-click it in Windows Explorer
  2. Choose Properties from the context menu
  3. Click the Unblock button in the lower right-hand corner of the resulting dialog
  4. Hit OK or Apply

Important: ZIP files should be "unblocked" before their contents are extracted.

1425.FilePropertiesUnblock.png

Note: Depending on the security policy level on the system, you may need to perform the same action for the DDLs once uncompressed.

Microsoft Windows 10

To restart the service by

  1. Opening the service windows
  2. Select the SmartconnectorService entry
  3. Either click on the Restart button, or Stop then start

service windows.png

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 19589
  • DavidKendrick21
  • MaximeLaudren21
  • smartconnector
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore