Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Troubleshooting sending emails using WireShark

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Troubleshooting sending emails using WireShark
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • RobertAndriolo
    RobertAndriolo
  • Benji
    Benji
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4689 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting sending emails using WireShark

Picard Product_Support
‎2018-09-11 07:52 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:47 AM

Issue

Sometimes just looking at the error message you get from e.g. TAC Vista or SmartStruxure when you try to send an email and it fails can lack information.

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

  • TAC Vista
  • SmartStruxure
  • WireShark

Cause

It is not necessarily all SMTP error messages and their explanation that are implemented in the software.

Resolution

For general information on WireShark usage read Using WireShark to analyse communications on an Ethernet network.

If McAfee antivirus with HIPS is installed on the PC, use RawCap to capture the communication, as you will not see traffic originating from your PC online in WireShark.

Additional reference for this article: Enhanced SMTP status codes

 

First of all when working with WireShark logs, it's a good idea to filter and focus the communication type you want to look at. In this case it's SMTP, so simply type smtp in the display filter and hit enter.

 

The easiest way to isolate a single smtp "conversation" between client and server, is to find one of the packets in the conversation, and in the "Analyze" menu click on "Follow TCP Stream".

 

This will give you the complete conversation in a separate window.

 

When you have used "Follow TCP Stream" be sure to set the display filter to "smtp" again when closing the window.

 

This is what happens if authentication is needed by the SMTP server but the client is not using authentication.

 

Here is the same attempt to send an email, but this time the client has enabled authentication

 

A little trick when using authentication is that WireShark can actually decrypt the Base64 encoded username and password. Simply right click on any SMTP packet, click "Protocol Preferences" and click "Decrypt AUTH parameters".

 

He are the packets decrypted

 

An error not easily detected by e.g. TAC Vista is error 535 "Incorrect authentication data". As stated in the enhanced status code table linked above, it simply means that either username, password or both is incorrect.

 

Though the product used may not have support for SSL and TLS, you can encounter SMTP server requiring it.

Here is an example of a SMTP requesting SSL

 

 

For further info on troubleshooting sending emails from TAC Vista, please read Troubleshooting Sending Emails from a Vista Server.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 16250
  • HernanUruena23
  • HernanUruena24
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore