Troubleshooting logon / display issues with the Mobile App Building Operation Technician Tool ("SmartBldgOp")

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Troubleshooting logon / display issues with the Mobile App Building Operation Technician Tool ("SmartBldgOp")
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2399 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting logon / display issues with the Mobile App Building Operation Technician Tool ("SmartBldgOp")

Picard Product_Support
‎2018-09-10 11:27 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:20 AM

Issue

  1. Can not logon with the Mobile App Building Operation Technician Tool.  Logon screen appears but app closes after selecting Logon
  2. No objects are displaying in my Custom View folder or other locations 
  3. Can not view or acknowledge alarms
  4. My alarm display colors as set in Workstation are not displaying correctly in the mobile app 

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Technician Tool 1.0.0 / 1.1.0
  • Building Operation Enterprise Server and SmartX Server 1.9.3 and below

Cause

May be various cause that are not allowing the Mobile App to connect to the server (Enterprise or Automation Servers), including EcoStruxure Web Services (EWS) Configuration Setting, folder names, User permissions and Alarm configuration.  Please review the different options below for assistance.

Resolution

Please note:

Mobile experience to be replaced with EcoStruxure™Building Operation v2.0 WebStation

For further information, please refer to Notice of Withdrawal of the Building Operation Technician Tool

 


When logging into the Technician Tool it times out

This has been seen before and was caused by the Windows Firewall. If you are able to ping back and forth between the enterprise server and iPad/iPhone, then it may be a firewall issue. You can either shut down the Windows Firewall or use Creating Windows Firewall rules to allow StruxureWare Building Operation to communicate on the TCP p... to set up firewall rules. 


Unable to connect to server or "Contact  technical support" message given

When logging in to the Technician Tool, specify the HTTPS port in the SERVER field (EX: 192.168.10.20:446).

 

The mobile app uses the feature from Building Operation StruxureWare call EcoStruxure Web Services, as such a majority of issues can stem from this setting.  If you are having issues logging into the Enterprise Server or Automation Server using the Technician Tool check the following:

  1. Software installed on both the Enterprise and Automation Servers must be 1.3.0.938 or later?
  2. Ensure the EWS Server Configuration settings are enabled in the server.
    1. As a minimum Serve Value and Serve Alarm must be set to true
    2. Browse allows object to browsed if not set, no objects will be displayed
  3. Ensure the user has sufficient permission to log in and MUST be member of the default domain

Values are not displaying in the Custom View folder or other locations

  1. Custom View folder must be located in the root directory of the Enterprise Server
  2. Check the EWS Configuration settings and ensure Browse is set to true - refer to item 2.2 above.
  3. In the EWS Configuration there is a tab labeled "Filter Hardware Folder"; Filters can be assigned By Path or By Object, check that the nominated folder or object has been filtered.

Can not view or acknowledge alarms

  1. In the EWS Configuration settings ensure that the Alarm Acknowledge setting is set to true.
  2. Also check that the Alarm has no additional 'Enforcement', such as Cause / Action - these alarms can only be acknowledge through Workstation.

My alarm display colors as set in Workstation are not displaying correctly in the mobile app

  1. Unfortunately the Alarm colors are hard coded within the Mobile App - this feature may be provided in a future release.  Date for this is currently unknown.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 12054
  • login
  • MahmoudSayed23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore