Troubleshooting 0x8000001e / 0x00001408 errors in Continuum BACnet controller error logs.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Troubleshooting 0x8000001e / 0x00001408 errors in Continuum BACnet controller error logs.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • David_Kendrick
    David_Kendrick
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3194 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting 0x8000001e / 0x00001408 errors in Continuum BACnet controller error logs.

Picard Product_Support
‎2018-09-11 03:23 PM

Last Updated: Admiral David_Kendrick Admiral ‎2023-05-04 02:35 AM

Issue

During communication issues with a Continuum BACnet controller, a large amount of the following error messages are seen in the controllers' error log.


0x8000001e 0x00236400 0x08023a50 0x4c000000 0x00000000
BACnet request timeout
0x00001408 0x0023a600 0x080af632 0x000000bc 0x00000284
Not enough memory

Product Line

Andover Continuum

Environment

BACnet Controllers

Cause

Most likely due to incorrect configuration or excessive BACnet traffic..... or both.

Resolution

Check the following:

  1. What is the version of Controller Firmware being used in each controller? This needs to be checked against the Continuum Compatibility Matrix to ensure that it is compliant with the version of Continuum being used on the SQL Server
  2. Are BBMDs configured on this site? If so, where are they located and how are they configured?
  3. Confirm the "maxinfoframes" value currently set for all controllers.
    • By default, a bCX for example should be set to 8
    • By default, b3 controller should be set to 2.
  4. If these are different from the default then why this has been changed?
  5. Confirm the BACtMaxMaster value in each is set to the maximum b3 NodeID + 1. This defaults to 127 but can cause comms delays on a smaller network.
  6. Confirm that all controllers on the MSTP are configured for the same Baud Rate. Any talking at a different baud rate would seem like noise on the network and disrupt communications, resulting in many 1408 error messages.
  7. Check the COV increment on points. The default of 0 can cause too much traffic on the bus and should never be left at Zero
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 14648
  • DavidKendrick23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now