The status of a Forced BACnet value is not reflected in a Graphic or the Watch Window.
  • Enterprise Server (ES)
  • Automation Server (AS)
This is functioning as designed.
It was designed so that the "Forced" status for BACnet values would not be displayed in graphics or the watch window.
For a workaround using a PE Script program to show the forced icon for a BACnet value see How to show the forced icon for a BACnet value in a Graphic.
In EBO version 3.0.1 and later this issue only occurs on internal BACnet points, points which are located in the Application folder under the BACnet interface for the SmartX server.