The Modbus Server/client is unable to read the address of a 32-bit Modbus register in a Building Operation server
  • The Modbus Server/client is unable to read the address of a 32-bit Modbus register in a Building Operation server
  • PeterLarsen
    PeterLarsen
  • RobertAndriolo
    RobertAndriolo
  • RyanSuar
    RyanSuar
‎2018-09-11 06:26 AM
Last Updated: Administrator CraigEl Administrator ‎2023-07-10 05:57 PM
The Modbus Server / Client is unable to read the values from address of a 32 bit Modbus register in a Building Operation server
  • Building Operation server
  • Modbus
The original Modbus/JBUS protocol specifies the use of 16-bit integer registers for Analogue Inputs and Analogue Outputs. The number range able to be represented in 16-bits is:
Unsigned: 0 to 65353
Signed:     -32768 to 32867
In order to represent larger numbers, it is common for 16-bit registers to be combined to represent 32-bit or 64-bit numbers. When a Modbus Client or Server reads a 32-bit Modbus value, it will be reading two consecutive 16-bit registers. An error will occur if  two 32-bit Local Modbus registers are created in Building Operation using consecutive register addresses since only the starting modbus register address is used for the request.
When configuring 32-bit Local Modbus registers in Building Operation, the next register address should not be used. Create the next Local Modbus register using the 3rd available Modbus register address.
Tags (2)
  • 15765
  • PeterLarsen23