Sigma DNN Configuration for Flat Ethernet Networks

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma DNN Configuration for Flat Ethernet Networks
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • sesa125819
    sesa125819

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2165 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma DNN Configuration for Flat Ethernet Networks

Picard Product_Support
‎2018-09-07 02:52 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-04 11:25 PM

Issue

Guidance is required for configuring a Sigma Distributed Network Node (DNN) when connecting it to a "Flat" Ethernet network.

Product Line

Satchwell BAS & Sigma

Environment

  • Satchwell Sigma
  • Ethernet network
  • Ethernet or ARCnet subnets

Cause

General configuration advice for ensuring proper communication between Sigma controllers and the network via the DNN.

Resolution

  • What Is a Flat Ethernet Network?
    A flat Ethernet network is a network architecture where all devices share the same broadcast domain and IP subnet.

    • There are no routers or subnets separating groups of devices.
    • All devices can communicate directly without routing.
    • Typically uses a single IP range and subnet mask, such as 10.158.0.0/16.
    • Simplifies configuration but may lead to scalability and performance issues in larger environments.
  • Network Configuration

    • On a flat Ethernet network, the DNN requires only:
      • IP address
      • Subnet mask
    • These settings, along with the DNN’s “Default Server” information, should be configured using the Sigma Device Configuration Utility (SDCU).
  • Routing Configuration

    • RIP (Routing Information Protocol) is enabled by default on the DNN.
      • If RIP is enabled, the DNN will broadcast the route to the sublan.
      • If RIP is disabled, a persistent route must be manually added to the Sigma server.
      • Refer to the article: Persistent routing on the Sigma server for detailed steps.
  • Modifying RIP Settings via Pocket Terminal

    • Disable RIP on port 5:
      • Launch Pocket Terminal
      • Enter: RIPD 5
      • Click Send
    • Enable RIP on port 5:
      • Launch Pocket Terminal
      • Enter: RIPE 5
      • Click Send
    • Check RIP status:
      • Enter: RIPS
      • Click Send
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 3271
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore