Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Sharing thermostats among Xenta 102-AXs (Master-Slaves)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sharing thermostats among Xenta 102-AXs (Master-Slaves)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1512 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sharing thermostats among Xenta 102-AXs (Master-Slaves)

Picard Product_Support
‎2018-09-07 06:16 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 06:07 PM

Issue

How to share the thermostat data (room temperature, setpoints) among Xenta 102-AXs?

Product Line

TAC Vista, EcoStruxure Building Operation

Environment

Xenta 102-AX with or without plug-in

Cause

Using the wrong SNVT in Xenta 102-AX or sending the nvoEffectSetPt incorrectly will result in different unit behavior among Xenta 102-AXs.

Resolution

Assign the Xenta 102-AX wired with the thermostat to be the master (A), and other Xenta 102-AXs to be slaves (B to N). Use the built in SNVTs to transfer data from the master to slaves as shown in the diagram below.

Sharing space temperature

  1. Bind master's nvoSpaceTemp to slaves' nviSpaceTemp.
  2. Make sure set Node Minimum Send Time and Node Send Heartbeat to be a non-zero number. (Read more information in Values sent from a 102-AX via SNVT bindings are not making it to the receiving controller.)

Sharing setpoint

It is recommended to share the setpoint through the normalized nvoEffectSetpt in order to have the same unit behavior between the master and slaves. Read more information about how the nvoEffectSetPt is calculated and displayed in Xenta 102-AX Effective Setpoint (nvoEffectSetPt) Calculation.

The steps of sharing the setpoint among Xenta 102-AXs are listed below:

  1. Set occupied/unoccupied heating and cooling setpoints on the master and slaves. The suggestion is to use the same setpoints setting on the master and slaves if want all rooms to operate in the same manner.

    In Xenta 102-AX plug-in
    1. Select Operating Parameters tab.
    2. Set the Cooling Setpoint and Heating Setpoint to desired value

    Without Xenta 102-AX plug-in
    1. Find SCPTsetPnts under VAV_Controller.
    2. Set the Cooling Setpoint and Heating Setpoint to desired values.
       
  2. Set master's nviSetpoint under VAV_Controller to a desired temperature (eg. 72 °F or 22 °C).
     
  3. Set the nvoEffectSetpt to be normalized.

    In Xenta 102-AX plug-in
    1. Select Operating Parameters or I/Stat Configuration tab.
    2. Under Effective Setpoint Source choose Norm of Heating and Cooling Setpoint

    Without Xenta 102-AX plug-in
    1. Find UCPTvavSelection.ESS under VAV_Controller
    2. Set UCPTvavSelection.ESS to 1. (Default is 0: Actual Setpoint).
       
  4. Bind master's nvoEffectSetpt to slaves' nviSetPoint.
     
  5. Make sure set Node Minimum Send Time and Node Send Heartbeat to be a non-zero number. (Read more information in Values sent from a 102-AX via SNVT bindings are not making it to the receiving controller.)

 

Additional Suggestions:

If the number of slaves is more than 30, it is better to tier up the transaction as shown below.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4476
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore