Values sent from a 102-AX via SNVT bindings are not making it to the receiving controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Values sent from a 102-AX via SNVT bindings are not making it to the receiving controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • LeeCravens
    LeeCravens
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1991 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Values sent from a 102-AX via SNVT bindings are not making it to the receiving controller

Picard Product_Support
‎2018-09-07 03:21 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-19 07:26 AM

Issue

Values sent from a 102-AX via SNVT bindings are not making it to the receiving controller. Viewing the outbound SNVT on the 102-AX shows a value, but the inbound SNVT on another controller is invalid or a default value.

Product Line

TAC Vista, EcoStruxure Building Operation

Environment

  • Xenta 102-AX
  • LNS SNVT bindings
  • LonMaker
  • NL220

Cause

The Node Configuration parameters are set with a send heartbeat of 0 seconds, which tells the controller to never send an update on the output SNVT.  All 102-AXs come with a default send heartbeat of 0 seconds, so for them to function in an LNS network where they must send data to another controller, the send heartbeat must be set to something greater than 0 seconds.

Resolution

  1. Open the Xenta 102-AX device Plug-in
  2. Go to the Node Configuration Tab
  3. Set the Node Minimum Send Time (SCPTminSendTime) to a non-zero value. The range is 0-6553.4 seconds.
    • nvoSpaceTemp
    • nvoStatOccBtn
    • nvoSetPtOffset
    • nvoLocalOccLatch
    • nvoEmergCmd
    • nvoUnitStatus
    • nvoBoxFlow
    • nvoTerminalLoad
    • nvoEffectSetPt
    • nvoFlowControlPt
    • nvoOccpncyStatus
  4. Set the Node Send Heartbeat (SCPTmaxSendTime) to a non-zero value. The range is 0-6553.4 seconds.
    • nvoAirFlow
    • nvoAuxTemp1
    • nvoAuxTemp2
    • nvoUnvInput1
    • nvoUnvInput2
    • nvoUnvInput3
    • nvoUnvInput4
    • nvoCO2sensor
    • nvoFanLoad
    • nvoHeat1Load
    • nvoHeat2Load
    • nvoMotorPositn
    • nvoActualValue
    • nvoOAirFlowRatio
    • nvoAirPressure

It is typical to set the Node Minimum Send Time and the Node Send Heartbeat to 60 seconds and the Node Receive Heartbeat to 0 seconds.

102AX Node Config Tab.jpg

 

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4002
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore