Xenta 102-AX Effective Setpoint (nvoEffectSetPt) Calculation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Xenta 102-AX Effective Setpoint (nvoEffectSetPt) Calculation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • MikaelKrantz
    MikaelKrantz
  • DavidFisher
    DavidFisher
  • LeeCravens
    LeeCravens
  • PeterLarsen
    PeterLarsen
  • Anonymous user
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2777 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Xenta 102-AX Effective Setpoint (nvoEffectSetPt) Calculation

Picard Product_Support
‎2018-09-07 04:23 AM

Last Updated: Guinan MikaelKrantz Guinan ‎2025-10-31 06:09 AM

Issue

  1. The nvoEffectSetPt is different than the nviSetPoint
  2. The nvoEffectSetPt is different than the cooling or heating setpoint (SCPTsetPnts)

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

Xenta 102-AX

Cause

The nvoEffectSetPt is calculated according to nviSetPoint, cooling or heating setpoints (SCPTsetPnts), nviStPointOffset, and thermostat offset.

Resolution

The nvoEffectSetPt is a SNVT network output in Xenta 102-AX and represents the current effective setpoint that the controller is utilizing in its control loop.

nvoEffectSetPt can be configured to display in two different manners: Actual and Normalized. (As defined bynciVAVselctcCntl.oP.ESS (UCPTvavSelection))

  • Actual nvoEffectSetPt displays the setpoint that corresponds to the currently active application mode of the controller (occupied cooling, unoccupied cooling, standby cooling, occupied heating, unoccupied heating, and standby heating).
  • Normalized nvoEffectSetPt displays the average of the cooling and heating setpoints for the currently active occupancy mode (occupied, unoccupied, standby).

NOTE: Whether nvoEffectSetPt is set to Actual or Normalized only affects how the effective setpoint is displayed and does not affect how the application operates. The 102-AX application utilizes the setpoint that corresponds to the currently active mode (occupied cooling setpoint, etc.). In addition, the thermostat adjustment of the setpoint will not appear in any SNVT in Xenta 102-AX controller. This offset is captured in the Xenta 102-AX's memory, and although it is not displayed, it is utilized into the nvoEffectSetPt calculation.

Also note that the below scenarios only apply to the occupied and standby modes since the unoccupied setpoints are unaffected by nviStPointOffset, nviSetPoint or by the thermostat offset.

  1. Scenario 1: nviSetpoint is unused

    1.1 Actual nvoEffectSetPt calculation:



    In this scenario, the nvoEffectSetPt is the sum of one(1) of the four setpoints (occupied cooling, standby cooling, occupied heating and standby heating) plus the offsets (nviStPointOffset and thermostat offset).

    1.2 Normalized nvoEffectSetPt calculation:



    In this scenario, the nvoEffectSetPt is the average of heating and cooling setpoints ( 1/2(Occupied Cooling Setpoint + Occupied Heating Setpoint) or 1/2(Standby Cooling Setpoint + Standby Heating Setpoint) ) plus the offsets (nviStPointOffset and thermostat offset).
     
  2. Scenario 2: nviSetpoint is used

    2.1 Actual nvoEffectSetPt calculation:




    In cooling mode, the nvoEffectSetPt is the nviSetPoint plus half of the difference between cooling and heating setpoints ( 1/2(Occupied Cooling Setpoint -Occupied Heating Setpoint) or 1/2(Standby Cooling Setpoint - Standby Heating Setpoint) ),  plus the offsets (nviStPointOffset and thermostat offset).

    In heating mode, the nvoEffectSetPt is the nviSetPoint minus half of the difference between cooling and heating setpoints ( 1/2(Occupied Cooling Setpoint - Occupied Heating Setpoint) or 1/2(Standby Cooling Setpoint - Standby Heating Setpoint) ), then plus the offsets (nviStPointOffset and thermostat offset).

    2.2 Normalized nvoEffectSetPt calculation



    In this scenario, whether the application is in the cooling mode or the heating mode, the nvoEffectiveSetPt is the sum of the nviSetPoint and the offsets (nviStPointOffset and thermostat Offset).

    Therefore, when nviSetPoint is used and nvoEffectSetPt is to Normalized, the actual heating and cooling SCPT setpoints do not matter; only the difference between them is significant. For example, setting occupied cooling and heating setpoints to be 75°F (24°C) and 65 °F (18°C) will give the same resulting nvoEffectiveSetPt as setting occupied cooling and heating to be 45°F (7°C) and 35°F (1°C).
     
  3. Example

    Occupied Cooling = 72°F (22°C), Occupied Heating = 68°F (20°C), nviSetPoint = 75°F (24°C), assuming the nviStPointOffset and thermostat offset are zero.

nvoEffectSetPt in Occupied Cooling or Heating Mode

 

Scenario 1.1

Scenario 1.2

Scenario 2.1

Scenario 2.2

Cooling Mode

72°F (22°C)

70°F (21°C)

77°F (25°C)

75°F (24°C)

Heating Mode

68°F (20°C)

70°F (21°C)

73°F (23°C)

75°F (24°C)

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4451
  • MikaelKrantz25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore