Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Shadow Schedule in AS isn't synchronized with the Lead Schedule in ES

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Shadow Schedule in AS isn't synchronized with the Lead Schedule in ES
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • sesa145087_brid
    sesa145087_brid
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2989 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Shadow Schedule in AS isn't synchronized with the Lead Schedule in ES

Picard Product_Support
‎2018-09-11 07:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:42 PM

Issue

When adding Shadow Schedule in AS, it isn't synchronized with the Lead Schedule in ES. This issue only happens when  there is an Exception schedule assigned with another Calendar added to the Lead Schedule in ES.

Error: "cannot verify lead object status"

Product Line

EcoStruxure Building Operation

Environment

  • SmartStruxure
  • Lead and Shadow

Cause

If a Lead Schedule contains an Exception with another Calendar assigned in ES, and a Shadow Schedule needs to be pointed to this Lead Schedule in AS, both the Shadow Calendar and Shadow Schedule need to be created and pointed to corresponding Lead Calendar and Lead Schedule. If only Shadow Schedule is created, it will fail to update to Lead Schedule, or even wipe the original setting with a blank schedule.

When involving Calendars the following should be considered:

  • The only way that the lead and shadow relationship can be maintained where calendars are concerned is where the calendar has the same name and is at THE SAME RELATIVE PATH as it does with respect to the lead schedule. Consider the following examples:
  • Example 1 - Lead Schedule is at Root and Shadow Schedule is at root and Referenced Calendar is at root. - under these conditions there is only a need for one Calendar object. The Lead Schedule has an exception that references the calendar at the root and everything works great.
  • Example 2 - Lead Schedule and Referenced Calendar are in Folder 1 and Shadow Schedule is in Folder 2. This will not work because the Shadow Schedule is trying to reference a calendar at the same relative path, i.e., in Folder 2, and there is none there.
  • Example 3 - Lead Schedule and LEAD Referenced Calendar are in Folder 1 and Shadow Schedule AND SHADOW CALENDAR are in Folder 2. This will work fine.
  • In simple terms keep the names and paths within the ES and AS consistent (the same) to avoid issues.

Resolution

Before the steps below, ensure the communication between AS and ES is OK. Refer to Binding between ES and AS or two AS shows Unresolved and Shadow Schedule in the Automation Server is not syncing to the Lead Schedule in the Enterprise Serve....

If the communication is fine, continue to the following steps:

  1. Create Lead Calendar and Lead Schedule in ES, and assign the Lead Calendar to the Exception of Lead Schedule (Should already done before).
  2. Create Shadow Calendar and Shadow Schedule in AS, and point them to corresponding Lead Calendar and Lead Schedule in ES.
  3. Now the Shadow Calendar should be able to synchronized with the Lead Calendar after changes have been made to the Lead Schedule.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 16441
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore