Setting up the override value to show the damper feedback on an i2/B3 866-V

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setting up the override value to show the damper feedback on an i2/B3 866-V
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3948 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setting up the override value to show the damper feedback on an i2/B3 866-V

Picard Product_Support
‎2018-09-07 02:27 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:57 AM

Issue

Setting up the override value to show the damper feedback on an i2/B3 866-v

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • i2/B3 866-V
  • Plain English
  • Script

Cause

Activate the damper position feature in the 866-V.

Resolution

SBO: See this video on creating a program that calculates damper feedback position. 

Also reference the article How to show damper feedback for an i2/b3 866-V which describes what needs to be done to show damper position and calibrate the damper. Sample objects, code and images showing configuration are supplied.

 

Continuum: There is a description in the 866-V installation manual on how to activate the damper position feature, but there are some additional pieces of information that this article has been created to address. This was initially to just get the feature working as mentioned in the next section below.

  1. Getting the damper feedback operational:
    Once the end stops are determined initially during the Learn process, the controller can then determine the position of the damper.
    1. Create a PE program to set the DamperOutput LCDState = Disabled and back to Enabled in the next line. This will run through its stroke to determine the end stops.
      ‘Example program named "damperstate"
      Fall thru, auto start
      ‘a 2 line program to initialize the stops
      
      Line 1
      Set damper LCDstate to disabled
      goto 2
      
      Line 2
      Set damper LCDstate to enabled
      stop
      To run from the command line Run damperstate
      Note that the Feedback will not start working until the Damper has gone full stroke in both directions. This will take several minutes.
    2. Set the damper point to on or –on depending on the position so it will move
    3. Print Damper OverrideValue from a command line or display it on a listview of the damper output after adding the overridevalue column
  2. Self Calibration - The LCDState toggle actually activates the "self calibrate" process. It doesn't just enable the feature. It is necessary to know this because you will need to activate the self calibration again whenever the damper is manually moved using the red actuator clutch release button. Using the clutch can cause the damper position to be reported incorrectly. Periodic re-calibration should be as a part of normal procedure for the controller. Once the clutch is used, the damper position will still report, but the value may be incorrect.
  3. Re-calibrate recommendation- Use a PE program that recalibrates the damper (i.e. LCDState as mentioned in Section A) on manual command by the service technician on a power cycle or at the end of an occupancy period.

Note: For controlling the Damper motor output create an Infinity Output point of type Triac on Channel 1. It can then be opened / Closed like any other Triac output with the use of On, -On or Off commands

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 2845
  • b3866
  • i2866
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore