Requirement to set the BACnet max master setting on a SE8000 series room controller
  • EcoStruxure Building Operation Automation Server
  • SE8000
  • BACnet MS/TP
The BACnet max master setting is not available to be set locally on the SE8000 room controller
The max master setting of the SE8000 can be changed in EcoStruxure Building Operation Workstation.
  1. Add the SE8000 to the EcoStruxure Server
  2. Open the SE8000 device properties
  3. On the Advanced tab, change the Maximum master property (which is a read/write property) to the required value.