Issue
When SE7000/SE8000 Series Room Controllers are bound to the MPM via ZigBee, "Effective Occupancy" does not follow "Occupancy Command" if the COV box is checked.
Product Line
EcoStruxure Building Operation, EcoStruxure Building Expert
Environment
- SSL MPM
- SSL SE8000
- SSL SE7000
Cause
Data type mismatch
Resolution
Uncheck the COV box for Effective Occupancy