Replace 7792 (7790) and 7793 (7790A) LIU with 7798C

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replace 7792 (7790) and 7793 (7790A) LIU with 7798C
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AdamSteele
    AdamSteele
  • RobertAndriolo
    RobertAndriolo
  • Cody_Failinger
    Cody_Failinger
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • Tom_Poovey
    Tom_Poovey
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1993 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replace 7792 (7790) and 7793 (7790A) LIU with 7798C

Picard Product_Support
‎2020-10-20 06:44 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 10:58 PM

Issue

  • Separate a 7792 or 7793 into two 7798C
  • Split SAV files 

Product Line

TAC INET

Environment

  • I/NET Seven
  • 779x Controllers

Cause

Need to replace a 7792 or 7793 which has two station addresses and replace with two 7798C Controllers which have one station address

Resolution

To split the required SAV Files:

  1. Download and Extract the attached SAV_Split_EXE.zip
  2. Make a backup of the I/NET Seven system using DBCreate.
  3. Perform Station Save to all the required controllers
  4. Copy the SAV files that need to be split to the same location where the ZIP file was extracted too in step 1.
  5. Run the SAV_Splt.exe
    1. The commands are showing the Sav_Splt.txt file contained within the ZIP file and shown below
Purpose:
Use this tool to create two 7798 SAV files from a dual-station 7793
SAV file.

Syntax:
Sav_Split.exe (with no parameters will check all save files in the current directory and split 2 station 7793s.)
Sav_Split.exe LLSS (where LL = Link and SS = Station)

Result:
The resulting files will be named DCULLSS-0.SAV and DCULLSS-1.SAV.
Rename these files appropriately to match the link and station of
the 7798 into which each will be loaded.

Example:
SavSplit.exe 0906
Results: DCU0906-0.SAV and DCU0906-1.SAV

 

 

Finally check the split files using the "Work Offline" mode within I/NET Workstation.

Any issues or additional questions please raise a case with your local support
 

For SAV file upgrade information see How to upgrade bin and SAV files in I/NET controllers.

Labels (1)
Labels:
  • TAC INET
Attachments
SAV_Split_EXE.zip
Tags (6)
  • Find more articles tagged with:
  • 15720
  • discontinuation
  • discontinued
  • replacement
  • RobertAndriolo20
  • SAV_Split
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of