Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Rehosting a Vista 5 License on the FlexNet License Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Rehosting a Vista 5 License on the FlexNet License Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
5398 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Rehosting a Vista 5 License on the FlexNet License Server

Picard Product_Support
‎2018-09-10 05:00 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:14 AM

Issue

Instruction on how to use your Entitlement to rehost Vista 5 License onto a new host computer or dongle.

Product Line

TAC Vista

Environment

  • Vista 5
  • Dongle
  • Host ID
  • Flexnet Licensing
  • Entitlement
  • Vista Licensing website

Cause

Limited documentation exists for how to properly rehost a Vista license on the Vista licensing website

Resolution

NOTE: Please remember that 5.0.X license files are not backwards compatible with versions of Vista 5.1.X. If your current license files are 5.0.X you must install 5.0.3 or earlier to properly rehost your license.

  1. Log onto https://schneider-electric.flexnetoperations.com and enter your Entitlement or Activation ID. To obtain an unknown ID, follow instructions in Lost license Entitlement ID Vista 5.x.
  1. In the top corner of the Home Page Select LICENSE SUPPORT and List Licenses
  1. This Entitlements license(s) will be listed.
  2. Select the License you wish to rehost by checking the Tick box located just left of the License.
  3. In the Action Menu, Select Rehost.
  1. Select Add New Host.
  1. From the Server Host Dropdown, select either ETHERNET (MAC address) or VENDOR DEFINED (Dongle) depending on your site.
  2. Enter the Mac address or Dongle ID to be used in the textbox
    *note that a Dongle ID must be entered as "TAC_HL_ID=##########"
  1. Select OK
  1. The New Server Hosts will now be populated with the correct Host ID. Click Next.
  2. Select Verify to verify the Host ID is valid
  3. Select Rehost to generate the new License.
  1. From the main page, select the License you wish to retrieve by checking the Tickbox located just left of the License.
  2. Select View and Save To File or Email license to obtain the .lic file.

It may be a good idea to compare the old .lic file with the new .lic file in Notepad to ensure they contain the same features. It is possible that the site license was a combined license generated from multiple Entitlements. If this is the case, repeat the steps above for each Entitlement then follow instructions in Manually Consolidating License Files.

Labels (1)
Labels:
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 6765
  • HernanUruena24
  • PeterLarsen21
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore