Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Outlook 2007 and Outlook 2010 with Continuum email alarms

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Outlook 2007 and Outlook 2010 with Continuum email alarms
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • DavidFisher
    DavidFisher
  • Alan_Wood
    Alan_Wood
  • Chris_Asbury
    Chris_Asbury
  • Jonathan
    Jonathan
  • AdamSteele
    AdamSteele
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3657 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Outlook 2007 and Outlook 2010 with Continuum email alarms

Picard Product_Support
‎2018-09-10 12:41 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:06 PM

Issue

Does Continuum support Outlook 2007 and Outlook 2010 as the client for emailing alarms?

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation (v1.93 and above)
  • Microsoft Outlook 2007 (32-bit)
  • Microsoft Outlook 2010 (32-bit)

Cause

Sending out alarms as emails using Microsoft Outlook.

Resolution

Outlook 2007(32-bit) and Outlook 2010(32-bit) have been tested by QA with Continuum for emailing of alarms.
This is mentioned in the Cyberstation Installation guide.

  1. Outlook Express does not work and is not supported.
  2. MS Outlook/Exchange 64-bit is not supported across all versions. 

For specific information on how to set up emailing of alarms on your Cyberstation please refer to the Continuum Help available on your Continuum Cyberstation or see Creating an EventNotification Email and Page Distribution List.

Note:
Outlook 2013 and above has not been tested by SQA, but reports from the field are that it does work.
In the new versions of Outlook, they have changed the name of the "Personal Distribution List" to the new name of "New Contact Group"
Please see How to create a distribution list from your contacts in Outlook for info on how to set up these groups,

Labels (1)
Labels:
  • Andover Continuum
Tags (5)
  • Find more articles tagged with:
  • 1.9x
  • 2.0x
  • 2016
  • 5852
  • AlanWood22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore