Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Message sent from AS to Modbus device after online status is restored

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Message sent from AS to Modbus device after online status is restored
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • PeterLarsen
    PeterLarsen
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Jonas_Brissman
    Jonas_Brissman
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2612 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Message sent from AS to Modbus device after online status is restored

Picard Product_Support
‎2021-01-07 06:59 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2021-12-02 10:04 PM

Issue

When a Modbus device comes back online after being offline a message is sent from the Building Operation Server to the Modbus device which looks similar to:

WriteData TX on /dev/tac_comporta: 01 2B 0E 01 00 70 77
ReadData RX on /dev/tac_comporta: 01 AB 01 9E F0

This message can cause the Modbus device to restart or stop responding, is it possible to disable it?

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation 1.5.xand above
  • Modbus Device
    • Socomec Power Meters
    • Crompton Integra 1221 Power Meter

Cause

A feature was added in release 1.5 that is intended to read the device's identification (0x2B). It works by polling this function code (FC). If the Building Operation server does not get a valid reply to this message, it assumes it is not supported by the device and will not request this again. This is usually not a problem but some Modbus devices, such as those listed in the Environment above, are unable to handle this message and will stop communicating with the AS or ES.

Resolution

In Building Operation 2.0.4 and above the option to enable or disable the device identification request (Function code 2B) has been introduced, allowing the poll interval (and online detection) to be set.

Some devices will stop responding to poll requests if the device identification is enabled.

Once disabled the AS or ES and the device may need to be restarted to enable normal polling without any device identification request being sent and stopping the normal responses from the device.

 

Device indentification.JPG


In previous versions this message cannot be disabled, however, if device polling is disabled the device identification request won't be requested, which can be used as a work-around.
To turn off the device polling:

  1. Open Properties
  2. Set "Poll interval" to "Inhibit"

The trade-off with this workaround is that the online detection for the device is turned off, so the device will never go offline in Building Operation.

In some instances, the third-party Modbus device will need to be restarted to allow communication to resume.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 16840
  • PeterLarsen19
  • PeterLarsen20
  • PeterLarsen21
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of