Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

MSTP controllers go offline when changing the MaxMaster value in the Automation Server from it's default of 127.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MSTP controllers go offline when changing the MaxMaster value in the Automation Server from it's default of 127.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1811 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MSTP controllers go offline when changing the MaxMaster value in the Automation Server from it's default of 127.

Picard Product_Support
‎2018-09-06 08:40 AM

Last Updated: Administrator CraigEl Administrator ‎2022-10-16 06:03 PM

Issue

MSTP controllers go offline when changing the MaxMaster value in the Automation Server from it's default of 127

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Workstation
  • Building Operation Automation Server
  • MSTP Master Controllers

Cause

The MaxMaster value is being set lower than some or all of the MSTP controllers on the network

Resolution

EcoStruxure Building Operation supports MSTP Master controllers in the address range 0-127 (often refered to as the node id). The MSTP network is a token passing network where the token is passed around the network, until a controller has the token it cannot 'talk' to other devices.

 

The MaxMaster value is defaulted to 127 to allow all devices on the network to receive the token and reply to online status requests, send values etc. If the MaxMaster value is less than any of the MSTP Master controller addresses then those controllers never receive the token and cannot respond to online status requests.

 

The value for the MaxMaster needs to be equal to or greater than the highest addressed MSTP controller node id.  For example, if the highest node id=54 then the MaxMaster will need to be set to 54 or higher. For maximum efficiency the MaxMaster should be set 1 or 2 greater than the highest controller address, this allows for adding future devices without needlessly polling for many non-existent devices. 

 

Please refer to BACnet MS/TP Network Properties – Basic Tab or Configuring the MS/TP Network for b3 Communication 

Labels (4)
Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • TAC IA Series
Tags (3)
  • Find more articles tagged with:
  • 18454
  • b3
  • GavinHeward22
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of