MPM BACnet Integration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MPM BACnet Integration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4764 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MPM BACnet Integration

Picard Product_Support
‎2018-09-11 04:38 AM

Issue

How can objects of a SmartStruxure™ Lite network be made available as BACnet points to third party BACnet building management system (BMS)?

Product Line

EcoStruxure Building Operation

Environment

SmartStruxure Lite

BACnet

Cause

The BACnet protocol is always active, as long as the network cable is connected. However, two different BACnet options can be selected: IP or Ethernet. The default option is Ethernet and this will need to be changed if BACnet over IP is required.

Resolution

The BACnet protocol is always active, as long as the network cable is connected. However, two different BACnet options can be selected: IP or Ethernet. The default option is Ethernet.

  1. To verify or to change which BACnet protocol is currently in use, select the SmartStruxure Lite Manager that you want to configure from the left-side Network panel.
  2. Then choose the BACnet configuration list item.
  3. Define the Network Number (if the protocol selected is BACnet IP).

    Note:

    The Network number must be defined only on the monitor Manager. It shall be different then the Parent Network where the monitor is connected.

    A BACnet Device is uniquely located by a network number and a MAC address. Creating two or more B/IP networks, each with a unique network number, can be useful for limiting the propagation of local broadcast messages and for providing security by confining traffic to a particular geographic or logical area.

  4. Select the desired protocol type from the drop-down list between BACnet IP and BACnet Ethernet.

  5. Then choose an optional port number (if the protocol selected is BACnet IP). Default is 47808.

  6. Select the BACnet Priority of the BACnet write action of the SmartStruxure™ Lite's network monitor. Default is 10.

    Note:

    SmartStruxure™ Lite does not support BACnet Write Priority, per se. However, in Firmware version 2.4.x and newer, it is possible to assign the write priority for all SmartStruxure™ Lite BACnet points. Default value is 10, except if you upgrade a Manager using a version 2.3.x or older, BACnet priority will be 8, but can be changed.

  7. Click the Save button to apply the configuration changes.

  8. Click hit the Save All button to make the modifications permanent and reboot the Manager for the new options to enter into effect.

  9. Change the BACnet instance number of the Manager if required.

IMPORTANT

Each Manager must have a unique BACnet device instance number. A Manager device instance number can be changed by selecting the top-left icon inside the left-side Network panel.

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (1)
  • Find more articles tagged with:
  • 14001
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore