Issue
I/A Series R2 station installed on a JACE-645 retrofit board (TRD-RB-645) fails to run with the following errors
Product Line
TAC IA Series
Environment
- JACE-645 Retrofit Board (TRD-RB-645)
- I/A Series R2 version 2.301.535.v1
- I/A Series G3 version 3.6.406
Cause
The R2 station has not been upgraded to R2 version 2.301.535 using the dbadmin command in the Niagara console.
There are errors when converting the upgraded XML version of the station to SNS.
Resolution
Ensure that the R2 station is upgraded as per step 3 on page 4 of the Retrofit Board Niagara R2 Inst...