Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to test the NiCAD Battery on a Controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to test the NiCAD Battery on a Controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • RobertAndriolo
    RobertAndriolo
  • sesa139513
    sesa139513
  • Tom_Poovey
    Tom_Poovey
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2596 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to test the NiCAD Battery on a Controller

Picard Product_Support
‎2018-09-07 01:02 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:20 PM

Issue

There appears to be a low battery on the control board. How can the NiCAD Battery be tested on the controller to see if it needs to be changed?

Product Line

TAC INET

Environment

I/NET Seven

Cause

Possible low battery on control board.

Resolution

There are some checks you can make regarding the battery condition. The battery has a design life of 7 years and sometimes lasts much longer.

With power applied to a controller for at least 72 hours, take a DMM and measure the DC voltage across the battery. It should be in the neighborhood of 4.2-4.3 vDC.

Remove power from the controller board and take the same measurement again. The beginning voltage should still be between 4.1-4.3 vDC and should start slowly tapering off (a tenth of a volt over a period of minutes would be normal).

When the battery voltage reaches 3.6 vDC this is the threshold at which the battery can sustain the RAM memory. Any voltage below this value will subject the RAM memory to loss of data (+ - a tenth or two).

If the initial voltage with power applied to the controller is less than 4.0 vDC after 72 hours, the battery may need replacing.

If the battery voltage drops rapidly after power is removed from the controller, the battery needs replacing.

If the controller memory inexplicably gets lost (not counting power surges, brownouts, etc.) and a station restore is needed, the battery may need replacing. Normally the above-mentioned tests will show that the battery has lost its storage capacity.

The TAC part number for the White NiCAD battery that is on most of the I/Net Controllers is 01-2100-545. These batteries can no longer be ordered through the Customer Care department.

For further battery info please reference Replacement I/NET Controller NICAD Battery info.


 

Labels (1)
Labels:
  • TAC INET
Tags (3)
  • Find more articles tagged with:
  • 2987
  • inet
  • RobertAndriolo21
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore