Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How to change b3's mac ID using RoamIO service tool

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to change b3's mac ID using RoamIO service tool
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • AbeMeran
    AbeMeran
  • Chris_Asbury
    Chris_Asbury
  • BillNeville
    BillNeville
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2508 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to change b3's mac ID using RoamIO service tool

Picard Product_Support
‎2018-09-11 01:30 PM

Last Updated: Guinan RandyDavis Guinan ‎2022-02-08 09:34 AM

Issue

For various reasons, it is sometimes necessary to change a b3's mac ID.

For example, a b3 that is removed from a site and will later be used at a different site needs to have its mac id reset to factory default to avoid the possibility of introducing a duplicate mac id.

NOTE: To set the MAC ID to the factory default you need BACnet Service Tool version 1.110004 or newer.  

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • Continuum b3 Controller
  • Continuum Service Tool RoamIO2
  • BACnet Service Tool

Cause

The MAC ID needs to be set or changed on a b3 controller.

Resolution

IMPORTANT: If the b3 has previously been assigned a valid mac id then proceed to step #1.

If the b3 has factory default slave mac id then see  CHANGING MAC ID ON A BRAND NEW B3 FROM THE FACTORY below

  1. Make sure the b3 is disconnected from the MSTP network then connect the RoamIO2 directly to the b3 using the service port.
  2. Launch the BACnet Service Tool and de-select the 'By Networks' and 'BACnet only' menu options in the view menu.
  3. Click the green icon to make the RoamIO2 sync to the baud rate of the b3 and discover it.
  4. In the 'Tools' menu select 'Set Offline B3 Mac Id' as shown below. 
  5. In the 'Modify MAC Id' window enter the b3's serial number and the new mac id to be set then click Apply. (NOTE: To set the MAC ID to factory default enter 172, DO NOT USE ZERO)
  6. To set the MAC Id to the factory default you need BACnet Service Tool version 1.110004 or newer.
    Tested working on beta version 1.119903). This beta version is attached. Download it and remove the .txt at the end to make it a zip file, unzip then see the readme.txt.
  7. A feedback message 'Success! will be returned if the MAC id was changed EXCEPT when setting the MAC Id to factory default (172)
  8. When setting the MAC Id to the factory default you will NOT get SUCCESS feedback, this is because the default id of 172 is a slave id (chosen because in hex it is AC for Andover Controls). Slave Ids are not allowed to initiate communication on the MSTP network. So, as a result of that, the b3 is unable to report to the RoamIO2 that the id was successfully changed. A visual sign that the ID was changed to 172 is that the TD led on the b3's RS485 port will shut off.
  9. Disconnect and re-connect to have the RoamIO2 communicate with the b3 using the new MAC id (unless you changed it to the factory default of 172).

CHANGING MAC ID ON A BRAND NEW B3 FROM THE FACTORY

The RoamIO2 can also be used to assign a mac id to a brand new b3 which has a factory default mac id of 0xAC (172 decimal) but the steps are a little different.

In order for a RoamIO2 to be able to send communication packets to the b3, it first has to sync up with the baud rate of the b3, it does by listening and analyzing the packets sent by the b3 until it is able to determine the baud rate. As mentioned before, the factory default mac id of a b3 is slave id 172 which prohibits the b3s from sending out packets and makes it impossible for the RoamIO2 to determine the baud rate.

There are several ways to work around the baud rate issue...

  1. Set the baud rate manually.
    1. Click on the green icon to attempt to connect the RoamIO2 to the b3.
    2. You will get an error that the baud rate could not be determined, click YES to proceed anyway
    3. From the 'Tools' menu select 'Set B3 Baud Rate' and set the baud rate to what you believe the last baud rate was for the b3. (The factory default baud rate is 19200)
    4. You should now be able to set the mac id per the steps above.

NOTE: You may have to try all the baud rates until you find the one the b3 is operating at.

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Attachments
BACnetToolIPC_1119903Beta.zip
Tags (2)
  • Find more articles tagged with:
  • 17561
  • AbeMeran22
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of