Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Customized information display on the SpaceLogic Sensor

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Customized information display on the SpaceLogic Sensor
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • RandyDavis
    RandyDavis
  • Reza
    Reza
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2399 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Customized information display on the SpaceLogic Sensor

Lt. Commander Reza Lt. Commander
‎2021-06-14 06:40 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-03-06 12:07 AM

Issue

How to populate customized information on the SpaceLogic Sensor display

Product Line

EcoStruxure Building Operation

Environment

  • SpaceLogic Living Space Sensor
  • Building Operation Multi-purpose Controller
  • Building Operation Multi-purpose VAV
  • Building Operation Room Controller (RPC)
  • Building Operation Workstation

Cause

Additional information required on how to customize information to be displayed on the SpaceLogic sensor

Resolution

Note: This feature may not work in controller FW V4.00.x, due to know issue Custom value text is not displayed and/or updated on the SmartX sensor device, in this case please upgrade controller firmware to V5.00.1 or higher.

Before starting, make sure the Integrator Menu icon and the custom information page have been activated:

  • The Integrator Menu icon can be configured under "SmartX Sensor Device/ Display/ Button and Scene configuration" as shown in the screenshot below:Capture1.PNG
  • Turn on "Allow custom information page" under "SmartX Sensor Device/ Display /Advanced" tab. By doing this, the custom information page is created under the Integrator menu icon of SmartX Sensor Display:     

Capture.PNG

 

  • To show how to add custom information to the custom information page of SmartX Sensor display, create a sample script program, where DI1 is a digital input and Status1 is a string output.
    numeric input DI1
    String output Status1
    
    If DI1 = on then Status1="running" Else Status1="not running"​

    Capture.JPG

 

  • In this program, when DI1 is on, the Status1 gets the string value of “Running”, otherwise the Status1 gets the string value of “Not Running”.
    • DI1 is bound to a Digital Value (Green Arrows) under the Application folder and
    • Status1 is bound to the CustomValueText1 (Red Arrows) as shown below:
      Capture2.PNG

 

  • Open the Watch pane, under the View tab, and add Digital Value and CustomValueText1 (access it through the “SmartX Sensor Device/ Display/ Basic” tab) to it.  When the Digital Value is Active the Custom value text 1 shows “Running”.
    Pic3.jpg
  • On the SmartX Sensor, navigate to the custom page through the Integrator menu icon, this will show the “Running” string.
    Untitled.jpg
  • Likewise the “Not Running” string would be populated on the SmartX Sensor custom information page screen when the Digital Value is Inactive.

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • MahmoudSayed23
  • RezaAmirzadeh21
  • RezaAmirzadeh22
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore