Changing the Automation Server HTTP / HTTPS ports
  • Changing the Automation Server HTTP / HTTPS ports
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • Reza
    Reza
  • RyanSuar
    RyanSuar
  • RobertAndriolo
    RobertAndriolo
‎2018-09-10 11:30 PM
Last Updated: Lt. Commander Reza Lt. Commander ‎2022-08-19 10:41 AM
Changing the Automation Server HTTP / HTTPS ports, 1.3 or higher.
  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
There is a need to change the Automation Server's HTTP and/or HTTPS ports from the default ports of 80 (HTTP) and 443 (HTTPS).
The HTTP / HTTPS ports of the Automation Server can be changed from Struxureware/EcoStruxure Building Operation WebStation, requires SBO/EBO V1.3 or higher.
  1. From a web browser*, connect and log on to the Automation Server.
  2. After you have logged on, click on the 'Account menu' near the top right corner:
    1. EBO 4.0.3 or higher,
      2. From the network tab, you can change the HTTP / HTTPS ports. Network configuration 4.0.png
    2. EBO V4.0.2 or lower,
      1. From the "Options" select 'Device Configuration'.Device Configuration 3.3.png
      2. The TCP/IP configuration page should appear. From here, you can change the HTTP / HTTPS ports.  Network configuration 3.3.png
3. Perform a Warm Start on the Automation Server to apply the HTTP / HTTPS port changes to the server.
* Check supported web browsers for Struxureware/EcoStruxure Building Operation at the WebStation specification sheet, make sure to select the correct SBO/EBO version: WebStation (se.com)