Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Anti-passback (APB): Only receiving one / delayed transaction(s) even though multiple valid cards are presented to the reader

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Anti-passback (APB): Only receiving one / delayed transaction(s) even though multiple valid cards are presented to the reader
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1436 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Anti-passback (APB): Only receiving one / delayed transaction(s) even though multiple valid cards are presented to the reader

Picard Product_Support
‎2018-09-07 01:59 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:33 AM

Issue

Using anti-passback and the transactions are delayed by 5 (or more) seconds after the actual card is presented to the reader. During this period (while LED is green) no additional transactions are been recorded to AMT Transaction window. As a result of this the anti-passback is not working for the concurrent swipes. 

The interval time between 2 swipes in the controller is configured to 2 seconds. We have tried changing it to zero, but we are not seeing more than transaction within this period come through to AMT.

Product Line

TAC INET

Environment

I/NET Seven 2.xx – with Anti-passback

Cause

When using anti-passback this is usually caused when you have defined the Door Sense setting in the Door Editor and it is either physically not wired or not working. By default this setting is set to Normally Open.  

If you have this setting set to normally open or normally closed - the strike will remain energized until the system detects that the door has opened through the sense switch or the strike duration has elapsed, whichever occurs first, the default strike duration setting is 5 seconds.

This means any badges that occur during this time are ignored; (only when anti-passback is enabled). Changing the Intercard interval will not make any difference in this situation.

Resolution

If the door status is not been monitored, you must set the door sense to none. If you are monitoring the door sense then make sure that the door sense activates on each card presentation so that the system recognizes the individual as entering the ‘zone’, therefore allowing the next card to be read. 

Note: Implementing anti-passback also requires that you define access control zones. When you use Anti-passback in the true sense it is strongly recommended to use the door sense switch, this is to ensure the individual has actually entered that zone. In situations where this is not possible you can tell the system to ignore the door status by setting the door sense to none, it will then assume that the individual has entered the zone and provide the transaction thereof once the strike duration has expired.  In this case the door strike must be configured to suit the environment. Anti-passback requires that a door controller have both an entry reader and an exit reader. An elevator door controller will support only an entry reader, and therefore, will not support anti-passback.

Refer to TCON 300 Chapter 9 – Access Control Anti-passback section for further information. 

I/NET Anti-Passback (APB) rules may also be of assistance in setting up Anti-passback.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 4806
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore