Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Advanced Display units of measurement or time zone are incorrect

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Advanced Display units of measurement or time zone are incorrect
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • SharlinaRe
    SharlinaRe
  • Benji
    Benji
  • Cody_Failinger
    Cody_Failinger
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
2264 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Advanced Display units of measurement or time zone are incorrect

Picard Product_Support
‎2018-09-10 01:47 PM

Last Updated: Picard RobertAndriolo Picard ‎2022-08-30 09:28 PM

Issue

The units of measurement or time zone on the Advanced Display differ from what is displayed in Workstation or Webstation. 

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Advanced Display (AD v1 v2 v3)
  • Building Operation Technician Tool

Cause

If the language settings on the Advanced Display are not set properly, then the units of measurement and time zone can be displayed incorrectly. For example, the temperatures in EcoStruxure Building Operation WorkStation or WebStation may be in degrees Fahrenheit while the Advanced Display shows the values in degrees Celsius. 

Resolution

Ensure that the Language used by the Advanced Display is set properly to the region it is located.


Advanced Display V1&2

Note: The SBOTechTool supports English, French, Swedish, Finnish, German, and Spanish.

  1. On the Advanced Display, go to Settings. If you cannot open up settings, ensure the AD Link app is in the disconnected state first.
  2. Go to Controls > Voice and input methods > Language and input. Verify that the Language is set to match the region where the Advanced Display is located.

Advanced Display V3

WebStation uses the language settings of the operating systems to detect the units that should be used and the time display format.

To access the Advanced Display v3 language settings:

  1. Exit the Kiosk application and drag up up from the bottom of the screen1. exit kiosk and drag up.png
  2. Click Settings2. click settings.png
  3. Click System3. scroll down to system.jpg
  4. Click languages and input4. click languages and input1 .jpg
  5. Click Add a language5. click add language.jpg
  6. Reorder (Press and hold, then drag the desired language to position 1)6. reorder.jpg

To access the Advanced Display v3 Date & Time settings:

  1. From System, click Date & Time4. click Date & Time .jpg
  2. Click Select time zone and select the correct local time zone5. Select time zone.jpg
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 18593
  • CraigEllis22
  • graphic
  • matching
  • page
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore