Issue
A Xenta 121-FC controller setup as a 2 pipe system will not heat or cool even though the terminal load is showing a demand.
Product Line
TAC Vista
Environment
Xenta 121-FC
Cause
The Xenta 121-FC does not have a water temperature sensor wired into the device
Resolution
For this functionality to work automatically, a water temperature sensor must be wired into the U1 terminal on the FC-121.
The other alternative is to set the supply temperature via the SNVT nviSourceTemp. This can be done from a supervisory system that is feeding the water to the 121-FC.
To use the SNVT nviSourceTemp as a solution the correct heartbeat will be require to be set in the 121-FC.
Values sent from a Xenta 121 FC/HP via SNVT bindings are not making it to the receiving controller is a link on how to set that up.