We have just installed (4) PM5560 meters. All units are displaying negative KW. Electricians have checked wiring and believe the meters are installed correctly. Here is the readout on one of the meters;
Vavg 489.92 V
Iavg 16.16 A
Ptot -9.3417 KW
E Del 0.000 WH
Any ideas what to check?
Thanks
Link copied. Please paste this link to share this article on your social media post.
No reply from customer after a long time.
Charles
Link copied. Please paste this link to share this article on your social media post.
How about the Power Factor (per phase and total)?
And per phase Voltage and Current?
Thank you!