ION9000 VT wiring and meter config Question

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 VT wiring and meter config Question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
EE103
EE103
Cadet

Posted: ‎2025-02-20 02:36 PM

0 Likes
5
548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-20 02:36 PM

ION9000 VT wiring and meter config Question

I am looking for confirmation that the ION9000 is correctly wired and configured for voltage readings with the below configuration. The system in question is a 3-phase, 3-wire system with a neutral bond via low resistance ground. The phase-to-phase voltage is 34.5kV and the VT ratio is 34500:120. With the below configuration, ION setup gives the warning "PT Primary/nominal mismatch."

Metering Setup - Basic
PM1 Volts Mode: 4W-WYE

PM1 PT Prim: 34500.0
PM1 PT Sec: 120.0
Nominal Voltage: 19918.58

 

VT config

Labels
  • Labels:
  • ION9000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-02-24 08:51 AM

0 Likes
0
461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-24 08:51 AM

Hello @EE103 ,

When meter is in 4Wire Wye volts mode, the sag swell module will read the voltage RMS from the Line-to-Neutral voltage terminals by default. There is a setup register in the sag/swell module to use VLL always, this would force the module to ONLY use line to line voltages.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 5
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-02-21 08:49 AM . Last Modified: ‎2025-02-21 09:44 AM

0 Likes
0
521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-21 08:49 AM

Hi @EE103 

 

Nominal Voltage refers to the primary power system RMS voltage (line-to-line voltage for Delta
systems and line-to-neutral voltage for Wye systems).

In Wye system as shown in the image above, the PT primary and secondary are referenced to the Neutral, therefore, the PT primary is considered as VL-N which is supposed to be 19918.58(34500/√3).
The Nominal voltage is 19918.58 while the PT primary is entered as VL-L which is 34500.

 


Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-02-21 12:32 PM

0 Likes
2
507
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-21 12:32 PM

Hello @EE103 ,

A lot will depend on what the outputs of the VT are. Is the VLL output on the secondary side 120V Line to time, or 120V Line to Neutral? Depending on the answer to this you may have different options.

If VT output is 120 V Line-to-line, then options include ignoring the warning, there is nothing wrong with your settings. Just not a common way to configure a meter, which is why ION Setup is giving a warning. Another option is to change the PT settings. PT Ratio is 287.5 (34500/120), have PT Primary =19838, PT Secondary =  69. This way the nominal voltage is close to the setting in PT Primary.

If VT output is 120V Line-to-Neutral, then may need to check your PT primary setting as I think there is likely a mistake.

If you read meter's voltage values for Line-to-Line or Line-to-Neutral, do you see your expected values?

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
EE103
EE103
Cadet

Posted: ‎2025-02-21 01:31 PM

0 Likes
1
472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-21 01:31 PM

Thanks for the info Charles & Mehran.

The VT output is 120V line-to-line (Measuring with a multimeter between V1 & V2 gives 120V, measuring between V1 and VN gives ~69V) and I do get the expected values for Vab and Van in the meter with these settings. It sounds like the settings are correct, I am fine ignoring the warning so for the sake of accuracy I will leave the PT primary and secondary values as-is.

As a follow-up question, I would like to ensure that my configuration for generating COMTRADE files for voltage sag/swells. The goal would be to trigger a waveform capture and COMTRADE file generation when voltage exceeds +/- 5% of nominal (>36225V & <32775V) and reset the trigger at +/-3% of nominal (>35535V & <33465V). The current configuration is below, and with these settings it appears that the meter is currently in an active sag/swell state although the voltages are within the limits described above.

Alarming - Sag/Swell - Voltage
Enabled Selected

Nominal: 19918.58 Volts

Swell Limit: 105%
Sag Limit: 95%
Hysteresis: 2%
Alarm Priority: Info Only

Power Quality - Sag/Swell Logging
Data Logging: 100 Records
Waveform Logging: 30 captures @ 32x54, 7 pre-cycles

COMTRADE: 10

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-02-24 08:51 AM

0 Likes
0
462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-24 08:51 AM

Hello @EE103 ,

When meter is in 4Wire Wye volts mode, the sag swell module will read the voltage RMS from the Line-to-Neutral voltage terminals by default. There is a setup register in the sag/swell module to use VLL always, this would force the module to ONLY use line to line voltages.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities
Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2025-02-25 09:51 AM

1 Like
0
448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-25 09:51 AM

At present ION Setup will generate the warning if the entered V Nominal is outside of plus/minus 10% of the PT Primary setting so given that the PT primary setting is 34500 and the nominal is under 20000, that would be why its generating the warning.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of