Hello everyone,
I'm working with a Schneider TM200C24R PLC and experiencing an odd issue with Modbus communication. Here's the situation:
I’ve checked the following:
Has anyone encountered this type of issue with the Schneider TM200C24R or any Modbus device? Any help or suggestions would be greatly appreciated!
Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Hi @Husam270
This forum is related to Metering & Power Quality topics.
Kindly post your question on the Industry Automation and Control forum:
https://community.se.com/t5/Industry-Automation-and-Control/bd-p/industry-automation-control_forum
Best Regards,
-Mehran
L3 Expert Advanced Metering
Link copied. Please paste this link to share this article on your social media post.
Hi @Husam270
This forum is related to Metering & Power Quality topics.
Kindly post your question on the Industry Automation and Control forum:
https://community.se.com/t5/Industry-Automation-and-Control/bd-p/industry-automation-control_forum
Best Regards,
-Mehran
L3 Expert Advanced Metering
Link copied. Please paste this link to share this article on your social media post.
Is the cable you are using is a sheilded one. Try once connecting with a new cable and check. You can try reading the data by using any converter on both plc and the device. If both of them are communicating through modscan, then try communicating them again.
Check the data lengths also. Some times if it's a float value and you have given an address which is not available it may throw errors. Try reading one value with one block. If it gets communicating try add the other variables.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.