Hi, I am using SBO 3.1 with SmartX Ccontroller AS-P. I have few RTU modbus devices connected to the controller and trying to get data and not successful. After examining trace log, I see the device is not returning function code and the device address.
What can be done about this for AS-P to accept the response or is there any work around. The log portion is as below.
2022-03-26 07:05:38.204 [1699824512] nsp.pin.modbus.DeviceRequests Polling device id = 5
2022-03-26 07:05:38.205 [1699824512] nsp.pin.modbus.SerialTransport Sending request 3 to server (for 1 registers from offset 5) to device id: 5
2022-03-26 07:05:38.215 [1699824512] nsp.pin.modbus.TransportSerialRS485 WriteData TX on /dev/tac_comporta: 05 03 00 04 00 01 C4 4F
2022-03-26 07:05:38.221 [1699824512] nsp.pin.modbus.TransportSerialRS485 ReadData RX on /dev/tac_comporta: 24 08 10 A0 52 C2
2022-03-26 07:05:38.221 [1699824512] nsp.pin.modbus.SerTransport Flush buffer. Protocol error code = 10
2022-03-26 07:05:38.222 [1699824512] nsp.pin.modbus.SerialTransport Invalid response. (MODBUS_RESP = 10 Requested code (= 3). Requested offset 4 1 2
2022-03-26 07:05:38.222 [1699824512] nsp.pin.modbus.DeviceMonitorRequest Poll device id = 5 result = 3 current status = 0 failure count = 0
Link copied. Please paste this link to share this article on your social media post.
This looks like a known issue, defect #45976. Contact your local Schneider Electric support and request hotfix 3.1.2.11303 or upgrade to EBO 3.2.3.7000 or higher.
Link copied. Please paste this link to share this article on your social media post.
This looks like a known issue, defect #45976. Contact your local Schneider Electric support and request hotfix 3.1.2.11303 or upgrade to EBO 3.2.3.7000 or higher.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
@clicame1 you don't appear to be an EcoXpert and therefore don't have access to download the latest Consolidated Hotfix that includes the fix mentioned above. I see that you have already contacted your regional support team who will be able to guide you further.