Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

BACnet IP server communication failure

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • BACnet IP server communication failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
KlaudiaKl
KlaudiaKl
Explorer

Posted: ‎2022-03-23 05:04 AM . Last Modified: ‎2022-03-23 05:20 AM

0 Likes
2
4797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 05:04 AM

BACnet IP server communication failure

Hello!
I've got the issue with communicating Enterprise Server or Automation Server with BACnet IP server gateway (Modbus to BACnet IP Intesis: https://www.intesis.com/products/protocol-translator/modbus-gateways/modbus-rtu-tcp-bac-ibox-bac-mbm). I see it in the device discovery tab as an "Unconfigured Devices" (photo) and I can move the device to the system tree and see the properties, the name of device, the addres etc. but I can't see any variables and I cannot add them manually. We tested the gateway and it communicated with the room unit without problems - we added the registers, we tested read/write functions and it worked (we could change the setpoints, operation mode etc.). The only option I considered was that the gateway have the password and we can't delete it from the device. We entered that password in Workstation Building Operation (version 1.9) but the error "Reject unrecognized service" appeared. Is there other option to add the device and collect the variables from it?

276069710_952298888820578_5651180310290639705_n.jpg

Klaudia

 

Tags (5)
  • Tags:
  • automation server
  • bacnet ip
  • ecostruxure
  • english
  • Enterprise Server.Automation Server.BACnet IP.Modbus.1.9
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
markb_ci3
markb_ci3
Contributor

Posted: ‎2022-03-24 06:17 AM

1 Like
1
4760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-24 06:17 AM

Devices that come in as "Unconfigured" usually have a problem with compliance to the BACnet standard.

 

Items that must be unique:

BACnet Address (applies to MSTP)

BACnet Name (workarounds to this are available)

BACnet Device Instance

 

That last one is a deal breaker. BACnet communications won't work if multiple devices are responding to the same ID.

 

There can also be problems with how the device is responding to the "WhoIs" request from the AS-P.

 

Insert a managed switch with a mirrored port in line with the device and do a WireShark capture to see the packets.

 

A "Who-Is" must be followed by an "I-am" by the device and it will provide the device details to the AS-P such as manufacturer, and the read/write properties it supports. If this communication does not happen properly, the AS-P won't know what to do with the device.

 

Armed with a BACnet capture, you should engage the manufacturer to see if they can help.

 

Good luck!

Mark

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
markb_ci3
markb_ci3
Contributor

Posted: ‎2022-03-24 06:17 AM

1 Like
1
4760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-24 06:17 AM

Devices that come in as "Unconfigured" usually have a problem with compliance to the BACnet standard.

 

Items that must be unique:

BACnet Address (applies to MSTP)

BACnet Name (workarounds to this are available)

BACnet Device Instance

 

That last one is a deal breaker. BACnet communications won't work if multiple devices are responding to the same ID.

 

There can also be problems with how the device is responding to the "WhoIs" request from the AS-P.

 

Insert a managed switch with a mirrored port in line with the device and do a WireShark capture to see the packets.

 

A "Who-Is" must be followed by an "I-am" by the device and it will provide the device details to the AS-P such as manufacturer, and the read/write properties it supports. If this communication does not happen properly, the AS-P won't know what to do with the device.

 

Armed with a BACnet capture, you should engage the manufacturer to see if they can help.

 

Good luck!

Mark

Tags (1)
  • Tags:
  • english
Reply
KlaudiaKl
KlaudiaKl
Explorer

Posted: ‎2022-03-29 11:30 AM

0 Likes
0
4701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-29 11:30 AM

Hello!
Thank you so much for your reply. We found out that it was the problem with BACnet Device Instance number and with the connection to the internal network. Now we see the device as configured in the Workstation and we can read the values of the units registers. But we got another problem now - we can read the values of the input registers but we can't write data to the outputs - we can't control the unit. When we put for example value of the setpoint of temperature we got the validation error. Maybe it is a problem that the device have the password that can't be delete? Do you got any ideas what we could do to make it work well?

Best Regards,
Klaudia

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore