Smart-UPS RT 5000 XL - Critical Alarm
Good morning,
I came into work today and one of my 2 battery backups are throwing a Critical Alarm.
I am not really sure why - I am very new to dealing with battery backups and I have the power features on this backup the same as the other one and it is not throwing errors.
04/30/2019 06:12:50 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 04/30/2019 05:52:49 Device UPS: Bypass not in range ; high voltage. 04/30/2019 01:13:19 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 04/30/2019 00:51:08 Device UPS: Bypass not in range ; high voltage. 04/29/2019 18:47:26 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 04/29/2019 18:32:01 Device UPS: Bypass not in range ; high voltage. 04/26/2019 16:04:09 System NTP update successful. 04/22/2019 15:28:53 Device UPS: Self-Test passed. 04/22/2019 15:28:45 Device UPS: Self-Test started by automatic timer. UPS StatusSmart-UPS RT 5000 XLLast Battery TransferUPS battery testBattery Temperature83.8°FRuntime Remaining21min 8secUPS InputInput Voltage249.1 VAC @ 60.0 HzUPS OutputOutput Voltage208.0 VAC @ 60.0 HzLoad Current5.3 AmpsOutput VA21.9 %Output Watts28.9 %Battery StatusState of Charge100.0 %Battery Voltage217.4 VDCNum of External Batteries0If anyone can explain to me why this is happening and how I should go about fixing it that would be awesome.
I have done a few Google searches, but I have not been able to find anything that I think is what I am looking for in this scenario.Thank you!
- Labels:
-
Back-UPS & Surge Protectors
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:59 AM . Last Modified: 2024-03-26 03:46 AM
Hi Chuck
Looking at the information you've included it simply is that your utility voltage is coming in at nearly 250 V and you have an output voltage of 208 V so it is information you that the UPS wouldn't be able to go to bypass (supply the load straight from utitlity power bypassing the UPS) because of this.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:59 AM . Last Modified: 2024-03-26 03:46 AM
Hi Chuck
If your load can handle 240 V then setting the output to 240v will definitely help. You may still see this message at times as a 10v difference between input and output is around the threshold but it will definitely reduce the message compared to the output being set to 208 V.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:59 AM . Last Modified: 2024-03-26 03:46 AM
Hi Chuck
Looking at the information you've included it simply is that your utility voltage is coming in at nearly 250 V and you have an output voltage of 208 V so it is information you that the UPS wouldn't be able to go to bypass (supply the load straight from utitlity power bypassing the UPS) because of this.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:59 AM . Last Modified: 2024-03-26 03:46 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:59 AM . Last Modified: 2024-03-26 03:46 AM
Thank you, Matt!
If I changed my output voltage on my UPS to 240V then, in theory, I should be fine right?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:59 AM . Last Modified: 2024-03-26 03:46 AM
Hi Chuck
If your load can handle 240 V then setting the output to 240v will definitely help. You may still see this message at times as a 10v difference between input and output is around the threshold but it will definitely reduce the message compared to the output being set to 208 V.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:59 AM . Last Modified: 2024-03-26 03:46 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:59 AM . Last Modified: 2024-03-26 03:46 AM
Thank you, sir!