Posted: 2024-08-12 11:15 AM
SMX3000HV ap9631
Problem with APC also re-flashed the APC again but still same problem, can't find any older firmware to flash back to test if the firmware is the problem below the log of the APC
Network Management Card AOS v7.1.2
Smart-UPS & Matrix-UPS APP v7.1.2
NMC Serial Number: 5A1613T36431
Model: Smart-UPS X 3000
UPS Serial Number: AS1739262992
Firmware Revision: UPS 07.4 (ID1003)
Date Time Name Contact Location System IP
08/12/2024 17:37:24 apcF7C145 Unknown Unknown 192.168.2.3
Date Time User Event Code
08/12/2024 17:37:24 apc SSH/SCP: File transfer started. 0x0037
08/12/2024 17:37:24 apc SCP CLI user 'apc' logged in from 192.168.2.87. 0x0014
08/12/2024 17:37:22 apc SCP CLI user 'apc' logged out from 192.168.2.87. 0x001E
08/12/2024 17:37:22 apc SSH/SCP: File transfer complete. 0x0037
08/12/2024 17:36:43 apc SSH/SCP: File transfer started. 0x0037
08/12/2024 17:36:43 apc SCP CLI user 'apc' logged in from 192.168.2.87. 0x0014
08/12/2024 17:27:07 Device UPS: UPS needs factory setup. 0x0192
08/12/2024 17:27:07 Device UPS: An internal UPS communication fault exists. 0x0172
08/12/2024 17:27:07 Device UPS: Restored the local network management interface-to-UPS communication. 0x0101
08/12/2024 17:26:49 System Network service started. IPv6 address FD10:7DDE:1665:C567:2C0:B7FF:FEF7:C145 assigned by router. 0x0007
08/12/2024 17:26:44 System Network service started. IPv6 address FE80::2C0:B7FF:FEF7:C145 assigned by link-local autoconfiguration. 0x0007
08/12/2024 17:26:42 System Network service started. System IP is 192.168.2.3 from manually configured settings. 0x0007
08/12/2024 17:26:38 System Network Interface restarted. 0x0002
08/12/2024 17:26:30 System Network Interface restarting. 0x0009
08/12/2024 17:26:30 System Web user 'apc' logged out from 192.168.2.87. 0x001F
08/12/2024 17:22:28 System SSH CLI user 'apc' logged out from 192.168.2.87. 0x001E
Home & Office - UPS & Software
Authentication Failed.
Posted: 2024-09-14 09:08 AM
The UPS is reporting a internal communication fault which may be due to internal components on the main circuit board of the UPS.
I would recommend performing a logic reset by following this article https://www.apc.com/us/en/faqs/FA156611/
If the UPS still has the same issue there might be an issue with its internal components. I suggest that you replace it
Specially if it no longer behaves properly
See article on basic Life expectancy of Single Phase UPS
https://www.se.com/us/en/faqs/FAQ000265093/
They offer trade in discounts for existing customers for SmartUPS and Symmetra UPS
https://www.apc.com/shop/tradeups/us/en/tradeups/overview.jsp