Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PowerChute Shutdown Issue

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • PowerChute Shutdown Issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
gonculator_apc
gonculator_apc
Explorer

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

0 Likes
7
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

PowerChute Shutdown Issue

I have an old desktop system running Windows XP SP3, which is not capable of correctly performing a Hibernate and recover, so I have Hibernate disabled. To replace a previous smaller UPS by another maker that never worked right, I just got a BE750G (Back-UPS ES 750). First I installed the PowerChute PE v. 2.0.0.0 software that came with it, then when I found a newer version on this site I uninstalled the earlier version and installed PowerChute PE v. 3.0.2. Then I performed a test of saving open files by opening several programs and creating new files, saving those files and then making changes WITHOUT saving the changes, then unplugging the UPS from the wall. When the PowerChute software went through the shutdown process, each open program in turn brought up the "Do you want to save the changes? Yes/No/Cancel" dialog (I did not type or click anything), then after several seconds the program closed. But after the shutdown was complete and I plugged the UPS back in and rebooted the system, I found that the file changes had not been saved. Is PowerChute 3.0 not capable of performing an unattended, fully-safe shutdown, or did I do something wrong or miss a step?

How can I correct this issue? Would reverting back to PowerChute v. 2.0 do it? I seem to remember some registry files in there about ADS or something like that (Automatic Document Save?), which are apparently not present in v. 3.0.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 750
  • back-ups
  • be750g
  • es
  • failure
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

No. Worksafe functionality does not exist in PCPE 3.X. As for is there a way to get automatic save without utilizing hibernate, maybe another member has a solution but I am not aware of one.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

Hi,

Hibernate - document save is provided by Microsoft as part of Windows XP hibernate is not incorporated / installed by PowerChute. When PowerChute is installed it enables hibernate so files will be saved when it commands the OS down. If you have disabled hibernate your documents will not be saved as you observed.

To verify I ran a test on XP SP3 with hibernate enabled. I created a Word doc, saved it and then added more lines of text leaving it open on the desktop. I also opened IE, PowerChute, and Excel and left them open. Set PowerChute to shutdown after on battery for 1 minute. Removed AC from the UPS and after being on battery for the minute a window popped up stating the system would be hibernated. The system powered down and after the 2 minutes delay the UPS switched for on battery to sleep mode. I restored AC to the UPS (BE750G) and the OS restarted since the BIOs was configured to do so. When the OS came back up IE, PowerChute, and Excel windows were as I left them as was the word doc that still included the unsaved lines of text.

When you say XP is not able to perform hibernate / recover properly what is the issue? Maybe there is a solution on Microsoft's technical support site for the issue you are seeing.

Reply

Link copied. Please paste this link to share this article on your social media post.

gonculator_apc
gonculator_apc
Explorer

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

There are two issues with my system and Hibernate, which may or may not be related. First, upon Hibernate, the system seems to save its state properly then attempts to shut down, but when it "shuts down", I get a screen full of garbage and the power does not turn off. Second, if I then manually power the system off and on, or reset it, it then attempts to wake from hibernation but gives an error message indicating that it failed. I'm then given the option to try again, or abort to a regular restart (and lose the saved hibernation state data). Only the regular restart works; it never successfully wakes from hibernation.

Will you please do a search through your archives for the term "WorkSafe"? I was under the impression that this feature included with or part of PowerChute PE (at least in version 2.0) was supposed to perform the function of automatically saving open documents, for systems that can not Hibernate. Was it removed from PCPE version 3.0 because it didn't work? Or is it still present, but not enabled in the same way (I believe it had to be manually enabled via a registry file with PCPE 2.0)?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

Hi,

I review the documentation for PCPE starting with version 1.0 and one of the key features listed for Windows XP is hibernation for file save. I cannot find any documentation for PCPE that list Worksafe with PCPE. We did offer Worksafe with PowerChute Plus (release notes link below) but not with PCPE.

ftp://ftp.apc.com/apc/public/software/windows/311/pcplus/424/relnotes.pdf

I suggest checking Microsoft forums and knowledge base articles to resolve the systems hibernation issue/s. I did a Google search on "hibernate not working Windows XP" and there are many hits for that subject. Normally I would recommend contacting Microsoft but they have ended support for XP so the web is the only option.

Reply

Link copied. Please paste this link to share this article on your social media post.

gonculator_apc
gonculator_apc
Explorer

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

Bill P. wrote:

I review the documentation for PCPE starting with version 1.0 and one of the key features listed for Windows XP is hibernation for file save. I cannot find any documentation for PCPE that list Worksafe with PCPE. We did offer Worksafe with PowerChute Plus (release notes link below) but not with PCPE.

ftp://ftp.apc.com/apc/public/software/windows/311/pcplus/424/relnotes.pdf

I suggest checking Microsoft forums and knowledge base articles to resolve the systems hibernation issue/s. I did a Google search on "hibernate not working Windows XP" and there are many hits for that subject. Normally I would recommend contacting Microsoft but they have ended support for XP so the web is the only option.

I have already unsuccessfully spent several days on the hibernation issue with this system a few years ago, and tried again for a while yesterday with only minor improvement. Now the system appears to hibernate normally, including shutting off completely at the end of the process. But on wake the progress bar seems to get all the way to the end, then the monitor goes off and indicates "No Signal" while the fans continue to run but the hard drive activity light remains dark, even if I leave the system alone for several minutes. Resetting or power-cycling the computer at that point gives the same result as before, it will not wake from hibernation and the only viable option is to choose to discard the hibernation data and perform a normal boot.

I have now uninstalled PCPE 3.0 and reverted to PCPE 2.0 to show you some things that your "documentation" seems to be missing. Below are some images for you: the CD that came with my UPS, the PowerChute folder as installed from this CD (I changed the default install location slightly, removing an unnecessary directory level), and part of the Troubleshooting page of the Help file (APC PCPE for XP.chm). Note the files in the folder named "Disable ADS.reg", "Enable ADS.reg" and "worksafe.exe". Also, there is a reference shown in the Help file by the entry "Open files are not saved" to "double click on the Enable ADS.reg file". Here is the content of that file:

APC wrote in file Enable ADS.reg:

REGEDIT4

[HKEY_LOCAL_MACHINE\Software\APC\APC PowerChute Personal Edition\2.00.000\Shutdown]

"WorksafeEnabled"=dword:00000001

So, let me rephrase my original question: Does the "Worksafe" or "ADS" functionality not exist in PCPE 3.0 for computers that can't Hibernate; or is such functionality built into it (rather than being provided in separate files like in 2.0), but for whatever reason not working on my system? Is it likely to work if I copy files and registry entries from 2.0 to 3.0?

2439_PCPE CD.jpg

2440_PCPE 2_0 Folder.jpg

2444_Help - APC PCPE for XP_chm.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

Hi,

As I wrote earlier one of the key features and benefits for PCPE on XP is integration with hibernation. My assumption is Worksafe.exe was included with PCPE 2.0 for systems that did not offer hibernation but I have no documentation on it. I installed 2.0 and checked help for Worksafe and it did not list anything. When I search on file save it list "hibernation" "hibernate" and "what happens during a prolonged power problem" and that recommends hibernation.

To answer your question Worksafe.exe is not included with PCPE 3.0. I don't know what would happen if you copied Worksafe.exe form 2.0 to 3.0. I am sorry that your system is messed up and hibernation does not work properly but I cannot recommend swapping files for 2.0 to 3.0 and editing the registry.

Reply

Link copied. Please paste this link to share this article on your social media post.

gonculator_apc
gonculator_apc
Explorer

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

0 Likes
0
2744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

Bill P. wrote:

To answer your question Worksafe.exe is not included with PCPE 3.0. I don't know what would happen if you copied Worksafe.exe form 2.0 to 3.0. I am sorry that your system is messed up and hibernation does not work properly but I cannot recommend swapping files for 2.0 to 3.0 and editing the registry.

That's not quite an answer to my question. I did not ask if the "worksafe.exe" file exists in PCPE 3.0, because I already know that it does not. I asked if the Worksafe functionality exists in PCPE 3.0. In other words, is there a way in PCPE 3.0, to get it to automatically save open, named documents before performing a "Shutdown" (not "Hibernate") of the system?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

0 Likes
0
2745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:00 PM . Last Modified: ‎2024-03-20 03:24 AM

No. Worksafe functionality does not exist in PCPE 3.X. As for is there a way to get automatic save without utilizing hibernate, maybe another member has a solution but I am not aware of one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore