PowerChute Shutdown with self test?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Shutdown with self test?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
K-Dog_apc
Lieutenant JG K-Dog_apc
Lieutenant JG

Posted: ‎2021-07-09 12:50 AM . Last Modified: ‎2024-02-14 11:33 PM

0 Likes
3
1978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 12:50 AM . Last Modified: ‎2024-02-14 11:33 PM

PowerChute Shutdown with self test?

If I have PowerChute configured to signal server shutdown when X amount of minutes runtime remaining, and I run a self test on the unit that has a significant load, does PowerChute recognize that this is a self test and not shutdown servers because the self test has discharged the batteries leaving less minutes in run time than my X value?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • self
  • test
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
K-Dog_apc
Lieutenant JG K-Dog_apc
Lieutenant JG

Posted: ‎2021-07-09 12:51 AM . Last Modified: ‎2024-02-14 11:33 PM

0 Likes
0
1979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 12:51 AM . Last Modified: ‎2024-02-14 11:33 PM

If I have PowerChute configured to signal server shutdown when X amount of minutes runtime remaining, and I run a self test on the unit that has a significant load, does PowerChute recognize that this is a self test and not shutdown servers because the self test has discharged the batteries leaving less minutes in run time than my X value?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 12:51 AM . Last Modified: ‎2024-02-14 11:33 PM

0 Likes
0
1979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 12:51 AM . Last Modified: ‎2024-02-14 11:33 PM

It depends on what PowerChute you're referring to. If you are running PowerChute Plus or PowerChute Business Edition, then no. You should get no indication of an on battery event other that self test in progress. Neither of these softwares should shut you down in this case.

If you're running PowerChute Network Shutdown, this should still not happen. I have ben at APC for 7 years and seen 2 issues with larger UPS units that may take a minute or more where the on-battery message was received but the self test information was not. The connected systems did end up shutting down.This by far is the exception however and not the rule. The reason this most likely happened is that the messages from the UPS are on a UDP port. They do not require the client respond to the event. That being the case, there is no way for the UPS to check to make sure the client received both messages.

A good rule of thumb however is to make sure your normal runtime at full charge is higher than your low battery signal time. If it is not, either lower the load, lower the low battery signal time, or in the case of older batteries, get new ones.

Reply

Link copied. Please paste this link to share this article on your social media post.

K-Dog_apc
Lieutenant JG K-Dog_apc
Lieutenant JG

Posted: ‎2021-07-09 12:51 AM . Last Modified: ‎2024-02-14 11:33 PM

0 Likes
0
1979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 12:51 AM . Last Modified: ‎2024-02-14 11:33 PM

thank you @SGT slaughter and @smarchet for your replies. My interest is primarily with 20, 40 & 80kw frames that are supporting an 80% + load and a self test may be run 2 or 3 times in an hour or so in the interest of trouble shooting a unit. Perhaps a good safeguard would be to unplug the data cable from the UPS NMC while self tests are running and batteries are being discharged below a possible low runtime threshold.

K-Dog

Reply

Link copied. Please paste this link to share this article on your social media post.

K-Dog_apc
Lieutenant JG K-Dog_apc
Lieutenant JG

Posted: ‎2021-07-09 12:51 AM . Last Modified: ‎2024-02-14 11:33 PM

0 Likes
0
1980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 12:51 AM . Last Modified: ‎2024-02-14 11:33 PM

If I have PowerChute configured to signal server shutdown when X amount of minutes runtime remaining, and I run a self test on the unit that has a significant load, does PowerChute recognize that this is a self test and not shutdown servers because the self test has discharged the batteries leaving less minutes in run time than my X value?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of