Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

New BR1500LCD question???

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: New BR1500LCD question???
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
5
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

New BR1500LCD question???

Hello, I just purchased a new BR1500LCD model. I took it out of the box, and connected the battery. After doing this, both the power on/off button, and display button were lit, but no beeps or anything. I plugged the unit in to the wall outlet, and then pressed the power on/off button. Nothing happened. The LCD screen remained off, and would not come on no matter how many times I tried. I checked to make sure the circuit breaker reset button on the back wasn't tripped, and it wasn't. I plugged a clock into the surge only outlets, and had power, but nothing on the battery backup outlets.

Anyway, I ended up chatting with an APC employee on line, and they told me to un-plug the UPS, and disconnect the battery again, and then connect the battery back up. I did this, and the UPS came to life. It started beeping four times to tell me it was on battery power. I then plugged it in, and could power on the LCD. It ran its little test, and everything is now fine, and the battery is charging. I also have power now on all outlets.

My question is, what was going on here? What caused it to act the way it did when I first connected the battery?

Thanks!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-22 03:58 AM

hmm very interesting. do you have a voltmeter to check the output voltage of the UPS from the battery back up outlets while the UPS is on battery? preferably a true RMS voltmeter..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

Hmmmm, after the battery symbol showed that the unit was totally charged, I ran a little test on it. I plugged a radio into the battery backup side, and un-plugged the UPS. I got the four beeps that let you know it's on battery backup, but no power out of any of the battery outlets.

Message was edited by: Keizer

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-22 03:58 AM

Ok, I just plugged a lamp into the battery backup side, and unplugged the UPS from the outlet. It runs the lamp just fine. Whats up with that?? Even with the UPS unplugged, and the lamp being powered just fine, the radio will not come on if I plug it in to the battery outlets.

Message was edited by: Keizer

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-22 03:58 AM

oh 😕

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-22 03:58 AM

I returned the UPS to the store and bought a different brand. The unit would also not power on occasionally. I have bought three APC brand UPS's over the years, and two have been faulty.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:43 AM . Last Modified: ‎2024-03-22 03:58 AM

hmm very interesting. do you have a voltmeter to check the output voltage of the UPS from the battery back up outlets while the UPS is on battery? preferably a true RMS voltmeter..

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore