Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Back-UPS RS 1500 - New Battery is Seemingly Bad?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS RS 1500 - New Battery is Seemingly Bad?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
158
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

0 Likes
9
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

Back-UPS RS 1500 - New Battery is Seemingly Bad?

I've had this unit for less than three years. Prior to my problems, I had roughly 20-25 minutes of battery run-time per PowerChute.

Approximately one year ago I encountered a power outage and the unit went to battery for approximately 10 minutes prior to all connected loads being disconnected and the unit turned off (I knew this was going to be an extended outage, so I decided to shut everything down). When the utility source returned, I powered everything up and PowerChute indicated that I had less than 5 minutes of battery run-time and that I should replace the battery. Today, about a year later, I finally got around to replacing the battery. Much to my surprise, I only have 6 or 7 minutes of battery run-time available. PowerChute says that the batteries are 100% charged and I have approximately 275W of load (out of 865W, or roughly 32% loaded). Are the brand new batteries I bought from APC bad? Is something else going on here? Am I overlooking something obvious?

I looked though the FAQ's and couldn't find anything useful.

Let me know if you need any additional information to help answer my question. Thanks in advance.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • back-ups
  • bad
  • battery
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:57 AM

0 Likes
0
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:57 AM

no problem!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

0 Likes
0
2414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

Thanks. I read that thread and I'll give it a shot. I'll post back in a day or so with an update.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

0 Likes
0
2414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

sure thing

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

0 Likes
0
2414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

most likely the batteries you have are fine. i would look at [this thread|https://community.exchange.se.com/t5/Home-and-Office-Forum/bd-p/home-office-forum] and follow the same suggestion that we are trying for this issue. the UPS may provide you with 20 or 25 minutes of runtime but thinks it only has 5 minutes or something. you can discharge the UPS completely until it turns off with the USB communication cable disconnected and then let the UPS charge back up so it realizes how much runtime it has. the runtime reported when the UPS is online is just an estimate so sometimes it can become inaccurate like this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

0 Likes
0
2414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

Didn't work. Still showing only 5 minutes of run-time with 285W of load.

I drained the battery using a lamp and a fan. Charged overnight with nothing connected. Connected everything this morning and powered on. Battery is at full charge according to PowerChute, but still minimal run-time.

Any other suggestions? Did I do something incorrectly?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

0 Likes
0
2414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:58 AM

how long did the actual battery last though for runtime?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:57 AM

0 Likes
0
2414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:57 AM

It ran on battery for at least 30 minutes. Somewhere between 30 and 45 minutes would be an accurate statement. There was approximately 100W of load. I'm confident in saying that the batteries are not the issue, but I would like to resolve the issue of PowerChute displaying the incorrect run-time so I can continue to use that program over Windows native UPS power management.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:57 AM

0 Likes
0
2414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:57 AM

unfortunately, i cant think of any other way to calibrate this. if this were a Smart UPS we could fix it but there is no way to do it on a Back UPS. even though it provides the amount of runtime, it'd have to be replaced if it does not report the correct runtime in the software even after the discharge/recharge process ๐Ÿ˜•

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:57 AM

0 Likes
0
2414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:57 AM

Thanks for your help anyway!

I may try the discharge / recharge method again, but with one change. I'd like to see what happens if I power my computer on at the beginning of the recharge period to see if PowerChute recognizes the small amount of charge on the batteries and adjusts the time remaining accordingly during the ensuing eight hours of charging.

Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:57 AM

0 Likes
0
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 12:43 AM . Last Modified: โ€Ž2024-03-22 03:57 AM

no problem!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore