Back-UPS Pro 550 not charging battery when powered on

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Back-UPS Pro 550 not charging battery when powered on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
aislinn_apc
Crewman aislinn_apc
Crewman

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-26 03:02 AM

0 Likes
21
26536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-26 03:02 AM

Back-UPS Pro 550 not charging battery when powered on

Hi!

I have a Back-UPS Pro 550. After replacing the battery, I realised that my unit was not charging the battery anymore when powered ON. Tests I have conducted so far:

  1. If the unit is powered ON, the battery does not charge
  2. When powered ON and I disconnect the battery I can measure 13.78V on the battery poles, so Voltage is there from the DC converter
  3. When I shut down the UPS, then the battery starts charging: I see the voltage slowly increasing and after 2 days the battery was 100% charged

Based on the above it seems to indicate that charging circuit is OK, but it might be a SW issue or some failing sensor that cuts battery charging ? Is there any reset function or FW update that I could apply ? Anything else I could check / do to fix it ?

The unit is around 5 years old so not covered by warranty but still not that old 🙂

Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • back-ups
  • battery
  • ups
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
aislinn_apc
Crewman aislinn_apc
Crewman

Posted: ‎2021-06-28 06:39 PM . Last Modified: ‎2024-03-26 03:02 AM

3 Likes
9
26507
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:39 PM . Last Modified: ‎2024-03-26 03:02 AM

On 11/19/2020 12:19 PM, Bill said:

You can try and brain dead the UPS to reset it.

Hi, thanks for the replies. I did try a brain dead reset + another type of reset I find on the internet, no success.

After opening the device I located a bad capacitor (see picture).

RIi4SY6UTtOVegTQ94LUtw%3D%3D.jpegRIi4SY6UTtOVegTQ94LUtw%3D%3D.jpeg

%2BiORiWL%2FhdQbLmD%2FaquOpA%3D%3D.jpeg%2BiORiWL%2FhdQbLmD%2FaquOpA%3D%3D.jpeg

After replacing it, the charging process of the Battery is working again!

Thanks for the quick answers and the help.

See Answer In Context

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 21
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-26 03:02 AM

0 Likes
0
26506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-26 03:02 AM

Hi,

You can try and brain dead the UPS to reset it.

See Schneider Electric FAQ FA158947 for instruction. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-26 03:02 AM

0 Likes
0
26506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-26 03:02 AM

the basic troubleshooting steps for the APC Back-UPS Pro with ... The Back-UPS is not connected to AC power, there is no AC power ... The battery will not charge if the temperature is over 50 degrees Celsius 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

aislinn_apc
Crewman aislinn_apc
Crewman

Posted: ‎2021-06-28 06:39 PM . Last Modified: ‎2024-03-26 03:02 AM

3 Likes
9
26508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:39 PM . Last Modified: ‎2024-03-26 03:02 AM

On 11/19/2020 12:19 PM, Bill said:

You can try and brain dead the UPS to reset it.

Hi, thanks for the replies. I did try a brain dead reset + another type of reset I find on the internet, no success.

After opening the device I located a bad capacitor (see picture).

RIi4SY6UTtOVegTQ94LUtw%3D%3D.jpegRIi4SY6UTtOVegTQ94LUtw%3D%3D.jpeg

%2BiORiWL%2FhdQbLmD%2FaquOpA%3D%3D.jpeg%2BiORiWL%2FhdQbLmD%2FaquOpA%3D%3D.jpeg

After replacing it, the charging process of the Battery is working again!

Thanks for the quick answers and the help.

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:39 PM . Last Modified: ‎2024-03-26 03:02 AM

0 Likes
0
26505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:39 PM . Last Modified: ‎2024-03-26 03:02 AM

I have the same problem with this model.

APC wont do anything. It seems to be a problem with this model.

I will give a try to search for the capacitor. Thx for the input.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Sandrus
Sandrus
Cadet

Posted: ‎2022-01-27 07:37 AM

In response to aislinn_apc
0 Likes
1
25444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-27 07:37 AM

Hi. I have the same problem with the same model. Which capacitor have you replaced?

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Keyro
Keyro
Cadet

Posted: ‎2022-01-30 10:05 AM

In response to Sandrus
0 Likes
0
25394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-30 10:05 AM

Hi, 
I´m also facing the same problem. After opening the device I found the same capacitor being dead as in the picture. You can recognize a dead capacitor by its curved top. In my device its labeled as the capacitor C18. You´ll need a 330uF 35V ELKO for that.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Venko
Crewman Venko
Crewman

Posted: ‎2022-02-11 07:25 AM

In response to aislinn_apc
0 Likes
0
25243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-11 07:25 AM

Hi ,

it also help me , but change two capacitors not only one

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

theone
Crewman theone
Crewman

Posted: ‎2022-02-28 03:54 AM . Last Modified: ‎2022-10-19 01:04 AM

In response to aislinn_apc
0 Likes
2
25054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-28 03:54 AM . Last Modified: ‎2022-10-19 01:04 AM

I have a similar problem:

https://community.se.com/t5/APC-UPS-for-Home-and-Office-Forum/Battery-charge-dropping-while-connecte...

 

Battery charging only during OFF and when ON battery is draining slowly even through connected to AC Mains input.

 

Got it open and capacitors seem fine

 

Any other suggestion?

 

IMG_20220228_141448.jpgIMG_20220228_141454.jpgIMG_20220228_141442.jpg

 

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Venko
Crewman Venko
Crewman

Posted: ‎2022-02-28 11:56 AM

In response to theone
0 Likes
1
25040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-28 11:56 AM

Hi ,

one capacitor in my ups looking fine but is only 270 uF and not working properly. After that i change it with new one 330 uF ups is working fine , only one capacitor is looking damaged  but i changed two of us.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

mr.Vox
Crewman mr.Vox
Crewman

Posted: ‎2022-09-13 12:42 PM

In response to Venko
0 Likes
0
22981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-13 12:42 PM

Very helpful. It happened firstly whilε the UPS was on a new 2 month battery. The battery fault started flashing together with the buzzer.. Turned off the unit and next day I got a new battery. I changed the battery and I thought everything is perfect.. Suddenly after a few  months  and  after an AC power loss Ι realized that the battery was not charged properly.. I will try doing a reset and check for problematic capacitors . This is an old UPS and I think  it reached its end of life. The problem is that I payed for New batteries.. They are not cheap and no fault errors appeared on the screen. Last battery is  CSB and previous was Yuasa. 

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

ivan06
ivan06
Cadet

Posted: ‎2022-12-19 10:35 AM

In response to aislinn_apc
0 Likes
0
22054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-19 10:35 AM

Thanks so much for this, mine had the exact same problem.

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

makksi
makksi
Cadet

Posted: ‎2023-01-01 06:08 AM . Last Modified: ‎2023-01-01 06:15 AM

0 Likes
2
21859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-01 06:08 AM . Last Modified: ‎2023-01-01 06:15 AM

I replaced 3 batteries and it was charging only one/two segments at first than zero. I was supposing it was because of battery. So now I understand the cause are capacitors. I unmounted the unity but I didn't see nothing clearly damaged. But now after reading this forum I will look more carefully.Do you know why capacitors get damaged?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

theone
Crewman theone
Crewman

Posted: ‎2023-01-01 06:55 AM . Last Modified: ‎2023-01-01 06:55 AM

In response to makksi
1 Like
1
21854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-01 06:55 AM . Last Modified: ‎2023-01-01 06:55 AM

The Aluminum Electrolytic Capacitors do not get damaged (usually) they age.

Lookup "Aluminum Electrolytic Capacitors aging" on google.

 

"... these capacitors degrade with age due to heating and evaporation of electrolyte. This process may take about 2 to 7 years depending on the application, ambient conditions and capacitor construction"

 

In my case there was no physical visual evidence of damage or aging (sometime they bulge and the top), but replacing them solved the problem.

After removing them I measured their capacitance and it was indeed lower than specified on them.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

makksi
makksi
Cadet

Posted: ‎2023-01-01 01:24 PM

In response to theone
1 Like
0
21836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-01 01:24 PM

Really thanks a lot I solved the problem after I was struggling since 2 years.I had exactly the 330uF capacitor with a dome on the top.I replaced it with a 470uF cap (the one I had immediately available) and now the battery charges at 100%!! It was charging below 20% before with a brand new battery! Thanks a lot! Do you know what circuit is this capacitor used for?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

yvesb
yvesb
Cadet

Posted: ‎2023-02-08 11:51 PM

1 Like
0
21231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-08 11:51 PM

Just a word to back this !

My Back-UPS Pro 550 (BR550GI) had the same issues.

 

- Battery indicator to low / 0% / 0 bars

- No alarm

- No "replace battery indicator"
- On a power outage, instant shut down

- Battery simply does not charge, without any indication

 

After reading this, I opened up my UPS. There was not "puffed caps" or any other visual clues.
As I'm not equipped to properly test capacitors, I decided to change the two 330μF capacitors anyway.

Having only 470μF, I used that.

 

The devices instantly stared charging again.

 

Thanks a @aislinn_apc , you just limited e-waste today ❤️

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

aislinn_apc
Crewman aislinn_apc
Crewman

Posted: ‎2023-02-10 12:03 AM . Last Modified: ‎2023-02-10 12:04 AM

1 Like
0
21206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-10 12:03 AM . Last Modified: ‎2023-02-10 12:04 AM

Thanks all for stopping by and dropping a thank you note 🙂 I am glad this helped rescue so many devices! I repaired 3 devices already, all working great.

But please note that I am no electrical engineer.... just a computer scientist with interest in tinkering with electronics, and who remembers the 2003-5 fiasco with broken capacitors so badly that looking at capacitors when electronic devices break became a second nature 🔍

I don't really know what these capacitors are used for in the circuit, which tolerance / spec they can be replaced with, if they should be replaced in pair, etc.... Keep that risk in mind when fixing your own device 😀

 

Maybe we have electrical engineers here who can help answer these questions!

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

giovannivl
giovannivl
Cadet

Posted: ‎2023-10-14 06:27 PM

1 Like
0
16584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-14 06:27 PM

Hello everyone!! My APC SMC1500C with 24 months warranty, I get error message b.04 after 25 months of use, just 1 month after warranty ends, funny right?, my local APC representation just says, no warranty nothing to do and this "kind" of HW does not has reparation just buy a new one, an APC almost of 500USD just stop working after two years.

 

But after change these condensers (original 330uF/25v to 470uf/35V) now it's working again! thanks!

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

TheSpy
TheSpy
Cadet

Posted: ‎2023-12-13 09:49 AM

In response to aislinn_apc
0 Likes
0
15130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-13 09:49 AM

Same problem, same solution, capacitor replacement. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

seesaw
seesaw
Cadet

Posted: ‎2024-02-11 07:36 AM

0 Likes
1
13448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-11 07:36 AM

I posted an article on Instructables website on this issue. I find these units all over the place. After seeing this post. I opened up one that was dead and was chronicly beeping solid. that one was blown fuses... so I removed the fuses (30amp) and replaced with miniature 20 amp to the back side.

I also pulled most of the caps out except for the (2) 4.7uF caps @ 450 Volt for the SMPS.

The caps I replaced are shown. I replaced the 22uF with 25uF with the orange tantalums. I measured all the caps and they were all below spec.

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

pserapp
pserapp
Cadet

Posted: ‎2025-01-28 07:03 AM

In response to seesaw
0 Likes
0
4371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-28 07:03 AM

Could you post a link to your article on Instructables? This is the only page I could find that discusses the b.04 error and how to fix it.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BobWar
BobWar
Cadet

Posted: ‎2025-02-05 12:53 AM

In response to aislinn_apc
0 Likes
0
4115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-05 12:53 AM

Many many thanks! Same problem, same solution.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of