Posted: 2021-06-28 06:38 PM
This was originally posted on APC forums on 11/19/2020
Hi!
I have a Back-UPS Pro 550. After replacing the battery, I realised that my unit was not charging the battery anymore when powered ON. Tests I have conducted so far:
Based on the above it seems to indicate that charging circuit is OK, but it might be a SW issue or some failing sensor that cuts battery charging ? Is there any reset function or FW update that I could apply ? Anything else I could check / do to fix it ?
The unit is around 5 years old so not covered by warranty but still not that old 🙂
Thanks
Posted: 2021-06-28 06:39 PM
This was originally posted on APC forums on 1/6/2021
On 11/19/2020 12:19 PM, Bill said:You can try and brain dead the UPS to reset it.
Hi, thanks for the replies. I did try a brain dead reset + another type of reset I find on the internet, no success.
After opening the device I located a bad capacitor (see picture).
After replacing it, the charging process of the Battery is working again!
Thanks for the quick answers and the help.
Posted: 2021-06-28 06:38 PM
This reply was originally posted by Bill on APC forums on 11/19/2020
Hi,
You can try and brain dead the UPS to reset it.
See Schneider Electric FAQ FA158947 for instruction.
Posted: 2021-06-28 06:38 PM
This reply was originally posted by Scott on APC forums on 11/20/2020
the basic troubleshooting steps for the APC Back-UPS Pro with ... The Back-UPS is not connected to AC power, there is no AC power ... The battery will not charge if the temperature is over 50 degrees Celsius
Posted: 2021-06-28 06:39 PM
This was originally posted on APC forums on 1/6/2021
On 11/19/2020 12:19 PM, Bill said:You can try and brain dead the UPS to reset it.
Hi, thanks for the replies. I did try a brain dead reset + another type of reset I find on the internet, no success.
After opening the device I located a bad capacitor (see picture).
After replacing it, the charging process of the Battery is working again!
Thanks for the quick answers and the help.
Posted: 2021-06-28 06:39 PM
This was originally posted on APC forums on 1/13/2021
I have the same problem with this model.
APC wont do anything. It seems to be a problem with this model.
I will give a try to search for the capacitor. Thx for the input.
Posted: 2022-01-27 07:37 AM
Hi. I have the same problem with the same model. Which capacitor have you replaced?
Posted: 2022-01-30 10:05 AM
Hi,
I´m also facing the same problem. After opening the device I found the same capacitor being dead as in the picture. You can recognize a dead capacitor by its curved top. In my device its labeled as the capacitor C18. You´ll need a 330uF 35V ELKO for that.
Posted: 2022-02-11 07:25 AM
Hi ,
it also help me , but change two capacitors not only one
Posted: 2022-02-28 03:54 AM . Last Modified: 2022-02-28 04:22 AM
I have a similar problem:
Battery charging only during OFF and when ON battery is draining slowly even through connected to AC Mains input.
Got it open and capacitors seem fine
Any other suggestion?
Posted: 2022-02-28 11:56 AM
Hi ,
one capacitor in my ups looking fine but is only 270 uF and not working properly. After that i change it with new one 330 uF ups is working fine , only one capacitor is looking damaged but i changed two of us.