APC Back UPS PRO 1000 -5 charge LED's flashing

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
rtom_it_apc
Cadet
0 Likes
3
164

APC Back UPS PRO 1000 -5 charge LED's flashing

This was originally posted on APC forums on 10/25/2012


I have an old but excellent APC Back UPS PRO 1000 . Last week I have seen Replace Battery light was on, so i got a new battery. In few hours it was charged but the 5 charge LED's flashing. What's happen?
This UPS is non PC connected with software.
Thanks for replay

Tags (1)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
166

Re: APC Back UPS PRO 1000 -5 charge LED's flashing

This reply was originally posted by Angela on APC forums on 10/26/2012


the procedure i provided is essentially a manual calibration.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
166

Re: APC Back UPS PRO 1000 -5 charge LED's flashing

This reply was originally posted by Angela on APC forums on 10/25/2012


i believe for this UPS it would indicate the runtime remaining is within less than two minutes of your low battery signaling time. that is generally what it means on other units. you may need to do a calibration to get this to recognize your new battery since it won't automatically.

i'd suggest that you plug in some non critical load, at least 30% and make sure it does not fluctuate. then i'd remove the UPS from AC power and let it run down until it turns off. then reconnect it to AC power (noting if the power really goes out, it won't get much runtime) and let it charge up for a day and see what you get. this will allow the UPS to discharge and recharge and re-calculate the available runtime.

was it flashing when the replace battery LED was on?

rtom_it_apc
Cadet
0 Likes
0
166

Re: APC Back UPS PRO 1000 -5 charge LED's flashing

This was originally posted on APC forums on 10/25/2012


I believe for this UPS it would indicate the runtime remaining is within less than two minutes of your low battery signaling time. that is generally what it means on other units. you may need to do a calibration to get this to recognize your new battery since it won't automaticall.

how can I do the calibration?

i'd suggest that you plug in some non critical load, at least 30% and make sure it does not fluctuate. then i'd remove the UPS from AC power and let it run down until it turns off. then reconnect it to AC power (noting if the power really goes out, it won't get much runtime) and let it charge up for a day and see what you get. this will allow the UPS to discharge and recharge and re-calculate the available runtime.

Tomorrow I try this procedure: is it an alternative to calibration?

was it flashing when the replace battery LED was on?

*No.
Thanks for replay*

BillP
Administrator Administrator
Administrator
0 Likes
0
167

Re: APC Back UPS PRO 1000 -5 charge LED's flashing

This reply was originally posted by Angela on APC forums on 10/26/2012


the procedure i provided is essentially a manual calibration.