I have a device that has a 6-20P plug (not the twist-lock L6-20P) that's current plugged into a 6-20R receptacle on the wall. This is in a business and I'm not sure if the power source is 208 three phase, or 240 single phase. All I know is that it's 6-20. I need to purchase a UPS to protect the device from brown-outs and surges.
I don't see any 230/240V APC models for the US, only 208V models with L6-20. If business's power source is 240 single/split phase, will the APC UPS's rated at 208V work? If this is the case then I will hire an electrician to make converter plugs to convert 6-20 to L6-20 so the UPS will plug into the receptacle and the device can plug into the UPS. Thanks
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:23 AM . Last Modified: 2024-03-14 12:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:23 AM . Last Modified: 2024-03-14 12:49 AM
I have a device that has a 6-20P plug (not the twist-lock L6-20P) that's current plugged into a 6-20R receptacle on the wall. This is in a business and I'm not sure if the power source is 208 three phase, or 240 single phase. All I know is that it's 6-20. I need to purchase a UPS to protect the device from brown-outs and surges.
I don't see any 230/240V APC models for the US, only 208V models with L6-20. If business's power source is 240 single/split phase, will the APC UPS's rated at 208V work? If this is the case then I will hire an electrician to make converter plugs to convert 6-20 to L6-20 so the UPS will plug into the receptacle and the device can plug into the UPS. Thanks
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:22 AM . Last Modified: 2024-03-14 12:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:22 AM . Last Modified: 2024-03-14 12:50 AM
I found converter plugs online so physically I know I can do it, I guess I'm just curious if there are any APC UPS's that will work with 240V split phase, which is pretty much what every american household has coming into it...
http://www.stayonline.com/detail.aspx?ID=8988
http://www.stayonline.com/detail.aspx?ID=11070
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:23 AM . Last Modified: 2024-03-14 12:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:23 AM . Last Modified: 2024-03-14 12:50 AM
Oh..
SURTD3000XLT
Nominal Output Voltage 208V
Output Voltage Note Configurable for 208 or 240 nominal output voltage
Nominal Input Voltage 208V
Input Connections NEMA L6-30P
Other Input Voltages 240
Thanks for steering me in the right direction... I think that was what I was looking for.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:23 AM . Last Modified: 2024-03-14 12:50 AM
Brian,
The SURTD3000RMXL3U can be configured as 240 Volts. There is also a backlpane option for this UPS with 2 X 6-20 outlets.
[SURTD3000RMXL3U |www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURTD3000RMXLT3U&tab=Options&total...]
[SURT011|www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURT011]
The Symmetra LX will do 240/120.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:23 AM . Last Modified: 2024-03-14 12:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:23 AM . Last Modified: 2024-03-14 12:50 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:23 AM . Last Modified: 2024-03-14 12:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:23 AM . Last Modified: 2024-03-14 12:49 AM
I have a device that has a 6-20P plug (not the twist-lock L6-20P) that's current plugged into a 6-20R receptacle on the wall. This is in a business and I'm not sure if the power source is 208 three phase, or 240 single phase. All I know is that it's 6-20. I need to purchase a UPS to protect the device from brown-outs and surges.
I don't see any 230/240V APC models for the US, only 208V models with L6-20. If business's power source is 240 single/split phase, will the APC UPS's rated at 208V work? If this is the case then I will hire an electrician to make converter plugs to convert 6-20 to L6-20 so the UPS will plug into the receptacle and the device can plug into the UPS. Thanks
Link copied. Please paste this link to share this article on your social media post.