apc device ip configuration wizard only gives serial, why?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • apc device ip configuration wizard only gives serial, why?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:34 PM . Last Modified: β€Ž2024-03-14 04:20 AM

0 Likes
7
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:34 PM . Last Modified: β€Ž2024-03-14 04:20 AM

apc device ip configuration wizard only gives serial, why?

I installed and ran APC Device IP Configuration Wizard v3.0.1 hoping it would detect the unconfigured network management card. I launch the app, click next, and am presented with two radio buttons: one for network configuring over the network and one for network configuring over serial port. Except the first one is greyed out! It will allow the serial port choice, but not the network based choice. Why?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:35 PM . Last Modified: β€Ž2024-03-14 04:20 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:35 PM . Last Modified: β€Ž2024-03-14 04:20 AM

Your welcome Neal, glad to here that it worked on another machine.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:34 PM . Last Modified: β€Ž2024-03-14 04:20 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:34 PM . Last Modified: β€Ž2024-03-14 04:20 AM

Well for whatever reason, trying it out on anohter machine did the trick. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:34 PM . Last Modified: β€Ž2024-03-14 04:20 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:34 PM . Last Modified: β€Ž2024-03-14 04:20 AM

Welcome to the APC Forum Neal.


What kind of APC Networking device are you using in conjunction with the Device IP Wizard? This is the first time that I've heard this kind of issue, we're using the same software and mine shows both option available. If you want to configure the device using a different method you can try this knowledgebase article [How do you make a Network Management Card communicate on a network?|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3061&p_created=1069703361&p...]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:34 PM . Last Modified: β€Ž2024-03-14 04:20 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:34 PM . Last Modified: β€Ž2024-03-14 04:20 AM

I'm actually not sure what kind of device it is. I'm sure I could have someone run to the server room go take a look. But the wizard never gets far enough to even go looking. I could understand if it just plain didn't find anything that needs configured. But I can't even do a network search. The button is greyed out. I am sure the wizard is coded to grey it out under certain conditions. Maybe its because I am running this on Windows 2003 server, and because the nic card on here is all manually configured to a specific address?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:34 PM . Last Modified: β€Ž2024-03-14 04:20 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:34 PM . Last Modified: β€Ž2024-03-14 04:20 AM

hi

just a couple questions from my end

did you download this from the web?
have you tried a different computer to see if it does the same thing?

i tried disabling my network connection to see if that would cause this issue, which i assume you DO have a network connection, but it still gave me the option to do it over the network.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:35 PM . Last Modified: β€Ž2024-03-14 04:20 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:35 PM . Last Modified: β€Ž2024-03-14 04:20 AM

Yup, download straight from APC web site.
Did not try another computer. Thats a fine idea. Will try that first thing tomorrow.
Yup this server has a working network connectin. I browsed the web just to make sure. πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:35 PM . Last Modified: β€Ž2024-03-14 04:20 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:35 PM . Last Modified: β€Ž2024-03-14 04:20 AM

Please do keep us posted.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:35 PM . Last Modified: β€Ž2024-03-14 04:20 AM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:35 PM . Last Modified: β€Ž2024-03-14 04:20 AM

Your welcome Neal, glad to here that it worked on another machine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.