SU3000 RM XL - SNMP shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU3000 RM XL - SNMP shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:21 AM

0 Likes
5
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:21 AM

SU3000 RM XL - SNMP shutdown

Hi,

in my office i use an APC SU3000 RM XL with Network Card

i have 3 debian server (no virtual macchine) and want shutdown them when ups run on battery and battery is low

i have some embeded PC for voip, running linux and stil want shut down it... mini pc have very low performance and need use light software

is possible do it by SMNP?

I never use this protocol, hope someone can help me 🙂

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:20 AM

0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:20 AM

I am not sure how I can help. You'll want to look into downloading a graphical UI MIB browser like GetIf or iReasoning but this likely will make more sense if you do some research on what a MIB is and the structure of it first so you know how to browse it. I am not sure if you researched that yet? It is called a MIB tree and the structure reflects that. There are different branches containing different products, components, and values at the deepest level. You kind of need to understand that stuff before you start browsing the MIB tree so you know what you're looking for.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:21 AM

0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:21 AM

Hi Marco,

You'll probably want to research SNMP and how it works a little bit. This will also maybe let you know about the two versions that exist and which is right for you.

Do you know what model of network card your UPS has by the way? That may impact which version of SNMP it provides.

The UPS will accept commands like shutdown and reboot over SNMP using an OID we provide within the APC PowerNet MIB. This MIB needs to be loaded within an SNMP Network Management Station that you'll have to load on your Linux system (maybe take a look at something like Nagios).

You can download the SNMP MIB you'll need from here -> http://www.apc.com/tools/download/index.cfm Look for Firmware Upgrades - MIB and download the PowerNet MIB (and not netbotz MIB). Once you download that, then you'll want to Browse the MIB and look for the UPS control OIDs.

I hope this helps get you started. Once you get rolling, there are OIDs you'll find to control the UPS. It will make more sense that you get started with these instructions before getting that far though as to providing you the OIDs. You'll need to understand research how to read a MIB.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:20 AM

0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:20 AM

You may want to install apcupsd on those linux machines. When registered with the NMC, the machines will get a signal to shut down when a power outage occurs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:20 AM

0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:20 AM

Hi,

thanks for your reply and patience Angela!

The card is an AP9617 (snmp v1-v3) fw 3.7.2

i start read this MIB

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:20 AM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:20 AM

Hi, angela

i try to read APC MIB...

but can you give me some help?

if possible, thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:20 AM

0 Likes
0
1107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:34 PM . Last Modified: ‎2024-03-14 04:20 AM

I am not sure how I can help. You'll want to look into downloading a graphical UI MIB browser like GetIf or iReasoning but this likely will make more sense if you do some research on what a MIB is and the structure of it first so you know how to browse it. I am not sure if you researched that yet? It is called a MIB tree and the structure reflects that. There are different branches containing different products, components, and values at the deepest level. You kind of need to understand that stuff before you start browsing the MIB tree so you know what you're looking for.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore