Weird behavior on SMT1000IC - "Battery Discharged", "Battery Charge in Range" all the time.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Weird behavior on SMT1000IC - "Battery Discharged", "Battery Charge in Range" all the time.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
gdarko
Crewman gdarko
Crewman

Posted: ‎2022-08-26 05:25 AM . Last Modified: ‎2022-08-26 05:27 AM

0 Likes
1
1030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-26 05:25 AM . Last Modified: ‎2022-08-26 05:27 AM

Weird behavior on SMT1000IC - "Battery Discharged", "Battery Charge in Range" all the time.

My unit uses the original APC RBC6 (2xGP12120 OEM) batteries and it is one year old, but was not used for several months. Since I started using actively few months ago, I am noticing those messages in PowerChute event log. It happens all the time with pauses, I believe this happens on load higher than 25%.

Month ago I did calibration, it shows me 45 minutes runtime. Self test passes. Once I stop the electricity in the house the UPS starts on battery just fine, show 40 minutes. Battery voltage according to PowerChute is from 26 to 27 VDC mostly.

 

What could be wrong or is this normal? I read APC Manual but couldn't nothing about this little mystery. I am open to replace the batteries but is that really needed?

 

Any help would be greatly appreciated.

 

 

8/26/22	14:12:49	Battery Discharged
8/26/22	14:12:46	Battery Charge in Range
8/26/22	14:11:44	Battery Discharged
8/26/22	14:11:42	Battery Charge in Range
8/26/22	14:11:39	Battery Discharged
8/26/22	14:11:35	Battery Charge in Range
8/26/22	14:10:12	Battery Discharged
8/26/22	14:10:07	Battery Charge in Range
8/26/22	14:10:02	Battery Discharged
8/26/22	14:10:00	Battery Charge in Range
8/26/22	14:09:42	Battery Discharged
8/26/22	14:09:40	Battery Charge in Range
8/26/22	14:09:28	Battery Discharged
8/26/22	14:09:20	Battery Charge in Range
8/26/22	14:09:08	Battery Discharged
8/26/22	14:09:06	Battery Charge in Range
8/26/22	14:09:02	Battery Discharged
8/26/22	14:08:53	Battery Charge in Range
8/26/22	14:08:39	User Logged On
8/26/22	14:08:32	Battery Discharged
8/26/22	14:08:12	Battery Charge in Range
8/26/22	14:05:31	Battery Discharged
8/26/22	14:05:28	Battery Charge in Range
8/26/22	14:05:24	Battery Discharged
8/26/22	14:05:16	Battery Charge in Range
8/26/22	14:04:48	Battery Discharged
8/26/22	14:04:46	Battery Charge in Range
8/26/22	14:04:30	Battery Discharged
8/26/22	14:04:21	Battery Charge in Range
8/26/22	14:04:19	Battery Discharged
8/26/22	14:04:04	Battery Charge in Range
8/26/22	14:03:54	Battery Discharged
8/26/22	14:03:50	Battery Charge in Range
8/26/22	14:03:32	Battery Discharged
8/26/22	14:03:30	Battery Charge in Range
8/26/22	14:02:58	Battery Discharged
8/26/22	14:02:31	Battery Charge in Range
8/26/22	14:02:24	Battery Discharged
8/26/22	14:02:18	Battery Charge in Range
8/26/22	14:02:16	Battery Discharged
8/26/22	14:02:14	Battery Charge in Range
8/26/22	14:02:06	Battery Discharged
8/26/22	14:02:04	Battery Charge in Range
8/26/22	14:02:02	Battery Discharged
8/26/22	14:01:58	Battery Charge in Range
8/26/22	14:01:22	Battery Discharged
8/26/22	14:01:02	Battery Charge in Range
8/26/22	14:00:48	Battery Discharged
8/26/22	14:00:46	Battery Charge in Range
8/26/22	14:00:40	Battery Discharged
8/26/22	14:00:38	Battery Charge in Range
8/26/22	14:00:34	Battery Discharged
8/26/22	14:00:30	Battery Charge in Range
8/26/22	14:00:10	Battery Discharged
8/26/22	14:00:00	Battery Charge in Range
8/26/22	13:51:26	Battery Discharged
8/26/22	13:51:18	Battery Charge in Range
8/26/22	13:50:52	Battery Discharged
8/26/22	13:50:26	Battery Charge in Range
8/26/22	13:50:24	Battery Discharged
8/26/22	13:50:16	Battery Charge in Range
8/26/22	13:50:10	Battery Discharged
8/26/22	13:50:07	Battery Charge in Range
8/26/22	13:50:00	Battery Discharged
8/26/22	13:49:58	Battery Charge in Range
8/26/22	13:48:52	Battery Discharged
8/26/22	13:48:50	Battery Charge in Range
8/26/22	13:45:06	Battery Discharged
8/26/22	13:45:03	Battery Charge in Range
8/26/22	13:45:00	Battery Discharged
8/26/22	13:44:58	Battery Charge in Range
8/26/22	13:44:52	Battery Discharged
8/26/22	13:44:48	Battery Charge in Range
8/26/22	13:44:38	Battery Discharged
8/26/22	13:44:36	Battery Charge in Range
8/26/22	13:44:30	Battery Discharged
8/26/22	13:41:52	Battery Charge in Range
8/26/22	13:41:44	Battery Discharged
8/26/22	13:41:36	Battery Charge in Range
8/26/22	13:41:24	Battery Discharged

 

 

 

 

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • battery
  • english
  • event log
  • rbc6
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-08-30 05:02 AM

0 Likes
0
1026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-30 05:02 AM

Hi @gdarko 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  May I please know the serial number of your UPS and are the batteries the original ones?

 

You mentioned that it wasn't used for a couple of months, how long was that?  Though it wasn't used, was it plugged in or you've unplugged it?  The reason I asked is that proper care should be done to batteries that will be stored.  Please see the articles below for your perusal.

 

Battery Discharge During Storage 

Battery Damage When Battery Is Left Discharged 

What is the expected life of my APC UPS VRLA battery? 

Why does a battery weaken when not in use? 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of