AP8659 Rack PDU 1: Communications lost.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP8659 Rack PDU 1: Communications lost.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
systeembeheer_apc
Crewman systeembeheer_apc
Crewman

Posted: ‎2022-08-26 12:23 AM

1 Like
3
1218
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-26 12:23 AM

AP8659 Rack PDU 1: Communications lost.

Hi this morning a smart PDU is starting to give errors...

 

08/26/2022 09:01:27 Rack PDU 1: Component communications lost with Outlet Board 3 Meter. Please verify that a terminator is inserted in either the In or Out port.
08/26/2022 09:01:27 Rack PDU 1: Component communications lost with Outlet Board 2 Meter. Please verify that a terminator is inserted in either the In or Out port.
08/26/2022 09:01:27 Rack PDU 1: Component communications lost with Outlet Board 1 Meter. Please verify that a terminator is inserted in either the In or Out port.
08/26/2022 09:00:11 Rack PDU 1: Communications lost.
08/26/2022 09:00:11 Rack PDU 1: Component communications lost with Phase Meter.

 

Devices connected are still online! And upgraded the PDU from version 7.0.6 to 7.0.8 still errors all the time!

Under about PDU outlet metering section gives no information and the load status is also empty???

Any help on further steps? or do i need to replace this unit?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-08-28 07:00 PM

0 Likes
2
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-28 07:00 PM

Hi @systeembeheer_apc 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. I am sorry to hear about the issue that you are having with our APC PDU, let's work on identifying the cause of it.

 

I understand that you are seeing communication lost messages on your PDU and that you have upgraded it to FW v7.0.8.  Let us check first if you have the CAN bus terminator installed on the PDU itself.

 

Let's perform a visual inspection on the PDU and reseat the terminator if you have one.  You may refer to the articles below to see where it should be installed and how does it look like.

 

  1. AP8XXX Rack PDU 2G "NMC CAN Bus Off" Error 
  2. No metering outlets detected" or "Lost Communication" error(s) on standalone AP84XX or AP86XX Metere... 

 

If the procedures above do not resolve the problem, we can proceed and reseat the display module.  If you have a spare PDU of the same type, we can swap a working display module into this PDU.  Will you be able to provide the serial number of your PDU as well?

 

You may refer to the article below to guide you on how to re-seat/swap the display module.  All loads must be disconnected and the PDU should be unplugged when doing this procedure.

 

Video: Why is my AP8XXX Rack PDU reporting communications lost with Phase Meter? 

 

I hope this helps.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

systeembeheer_apc
Crewman systeembeheer_apc
Crewman

Posted: ‎2022-08-29 11:08 PM

In response to JonPro
0 Likes
1
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-29 11:08 PM

Hi Jon, 

 

Thanks for responding! 

There is a terminator installed on the PDU can i remove it safe and put it back in without disconnecting the load?

A reboot of the network interface did not help!

 

And i dont have a spare PDU to swap the display module? 

What is your advise? 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-08-30 12:14 AM

In response to systeembeheer_apc
0 Likes
0
1181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-30 12:14 AM

Hi @systeembeheer_apc 

 

Can you DM me the serial number of your PDU unit?

 

Also, the terminator can be reseated if we cannot really schedule downtime at the moment.  Aside from powering down the PDU.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of