UPS will not take IP Address from APC Device IP Configuration Wizard.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS will not take IP Address from APC Device IP Configuration Wizard.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
3
3810
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

UPS will not take IP Address from APC Device IP Configuration Wizard.

We just installed Two new UPS’ and a Automatic Transfer Switch. All of which have Network Management cards.

I ran the APC Device IP Configuration Wizard and it found all 3 devices. I assigned them all IP Addresses and the Wizard did not error once. However on the UPS’ when the web interface came up it would not load. And the UPS’ would not respond to Ping. The Automatic Transfer Switch took the IP without error and is working.

I ran the Wizard again and it found the 2 UPS’ again. I tried to give them an IP and got the same thing. I have tried this 3 times now and every time it seems to give it the IP but the web interface will not come up and will not respond to ping. And then the wizard it will still see it as unconfigured.

We are working remotely trying to set this up so a serial cable will require travel time.

Can anyone help me with getting the UPS’ Management cards to accept the IP Addresses assigned by the configuration wizard?

Any help is appreciated

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • ap9630
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
3807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

We had that happen where it would not reply. We were required to use a serial cable to configure the management card unfortunately.

Other than that, we've configured about 5 cards now using the ARP method and it works each time.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
3807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

I have a couple questions for you:
1. What model of UPS are you using?
2. What model of APC Management Card are you using (AP9617 - Gen1, AP9630 - Gen2)?

If it is the AP9630, try following the attached document.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
3807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

That worked on one of the Units! The other unit took it at 1st and then when pinging the 1st two replyed and then it failed after that. its no longer displaying at all.

They are both
Smart-UPS 2200 RM XL
and the Maagement cards are AP9630

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
3808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

We had that happen where it would not reply. We were required to use a serial cable to configure the management card unfortunately.

Other than that, we've configured about 5 cards now using the ARP method and it works each time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore