UPS to plug into a Nema 15-30

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS to plug into a Nema 15-30
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:31 AM . Last Modified: ‎2024-03-12 03:00 AM

0 Likes
3
5468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:31 AM . Last Modified: ‎2024-03-12 03:00 AM

UPS to plug into a Nema 15-30

Sorry if this is a painfully stupid question but I've got a couple NEMA 15-30, 30A-250V receptacles in my datacenter and I'm wondering if there's any way to use this outlet for powering a rack?  I've googled around for a UPS that uses that plug with no luck.  I'm wondering if I can get a converter, or is that type of outlet used for specific types of appliances and no good for servers?

Thanks,

Isaac

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:31 AM . Last Modified: ‎2024-03-12 03:00 AM

0 Likes
0
5466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:31 AM . Last Modified: ‎2024-03-12 03:00 AM

This wing of the building is only 10 years old, but maybe it was a little misleading to call the room a datacenter, I'm not sure it was designed with that use in mind.  The building is a research lab for biological sciences so I'm guessing the 15-30s were put in for autoclaves or -80 freezers or some other science stuff.

I'll bug the electricians about converting those to L6-30 and price out some a UPS or two that takes L6-30.  Thanks so much for all the great information!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:31 AM . Last Modified: ‎2024-03-12 03:00 AM

0 Likes
0
5466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:31 AM . Last Modified: ‎2024-03-12 03:00 AM

This is a rare plug I haven't really seen or been asked about. This appears to be 3-phase too and all of our 3-phase stuff is around the same amperage and 5 wire (3 phases, ground, neutral) or the 4 wire stuff (3 phases, ground) like this receptacle is all higher amperage. I am most familiar with Rack PDUs and that is where my feedback comes from. I also was thinking most people at higher amperages look for locking plugs/receptacles and if it is 15-30R, it is a straight blade.

If you were to use a converter, you'd need something that is still 4 wire and supports 3 phase. Also, changing it out sounds involved for pulling new wires and stuff. I don't know if you have anything else available but it sounds easier not to use these. I asked around and nobody is really super familiar with it but I'll still try to dig a little bit. I feel like there must be a reason why you cannot find anything. Is the building old where these are? Just curious if it is something that is not typically used anymore and just has not been upgraded in your building/location.

Reply

Link copied. Please paste this link to share this article on your social media post.

roger_apc
Ensign roger_apc
Ensign

Posted: ‎2021-06-29 08:31 AM . Last Modified: ‎2024-03-12 03:00 AM

0 Likes
0
5465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:31 AM . Last Modified: ‎2024-03-12 03:00 AM

Hi Isaac,

You might want to take a magnifying glass to the receptacle.  I often find them very hard to read.  Having one of those in a data center would be extremely unusual.  They are typicaly only used for 3-phase motors that do not require a neutral.  2418_NEMA-15-30.pngA much more common outlet would be a L5-30 (120V 30A) or a L6-30 (208V 30A).  If it is either of those, APC makes several UPS units that would plug directly into the outlet.  But if it is truly a 15-30, any electrician should be able to convert it to a L6-30 at a minimal expense.  All it would take is a new outlet (25 bucks? at Home Depot) and a new circuit breaker (50-75? at HD) and about one hour of time.  The biggest expense in adding new outlets is installing the conduit and pulling new wires.  Unfortunately, since there is no neutral installed, it could not (legally) be converted into a L5-30.

For general reference:

if the first # is a 5, the voltage = 120 (in the US) 125 volts max  (May be color coded yellow)

if the first # is a 6, the voltage = 208 or 240 (in the US) 250 volts max  (May be color coded Blue)

The # after the - is the current (15, 20, 30, etc.)

Add an "L" in front, and it becomes a locking plug or receptacle.

Append a "P" or an "R" at the end, and you identify it as a plug or receptacle.

While 5 and 6 are the most common first #'s there are bunch of others.  In computer rooms, I've seen L14-30 (locking, split phase, 30A) and L21-20 (locking, 3-phase, 20A).  In fact, I think APC makes PDU's with those plugs, and I think one of the "default" outlets on the Symmetra LX series is a L14-30.

Hope this helps.

Cheers

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:31 AM . Last Modified: ‎2024-03-12 03:00 AM

0 Likes
0
5467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:31 AM . Last Modified: ‎2024-03-12 03:00 AM

This wing of the building is only 10 years old, but maybe it was a little misleading to call the room a datacenter, I'm not sure it was designed with that use in mind.  The building is a research lab for biological sciences so I'm guessing the 15-30s were put in for autoclaves or -80 freezers or some other science stuff.

I'll bug the electricians about converting those to L6-30 and price out some a UPS or two that takes L6-30.  Thanks so much for all the great information!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore