Posted: 2025-06-06 12:19 AM
Hello, our client has 3x APC Smart-UPS Ultra 5000 SKU: SRTL5KRM2UI. Due to that these UPS devices used to have critical problems, until we updated firmware, we have to document every little problem, and this week we had our first this year.. with one of devices.
Problem - On battery power in response to an input power problem [0008].
I understand that this is pretty common error, due to that electricity tends to behave strangely, but looking at the log, this error happened at the same time Self-Test started, and I have not seen this before, so I wanted to know, if this is some kind of a bug, or this happens from time to time. Errors like these in the middle of night might cause a panic.
Log:
| 06/03/2025 | 02:27:15 | Device | UPS is online. |
| 06/03/2025 | 02:27:15 | Device | No longer on battery power. |
| 06/03/2025 | 02:27:14 | Device | Self-Test finished. |
| 06/03/2025 | 02:26:53 | Device | Self-test started by the UPS. |
| 06/03/2025 | 02:26:53 | Device | UPS is no longer online. |
| 06/03/2025 | 02:26:53 | Device | On battery power in response to an input power problem [0008]. |
How should i document this problem. Thank you.
Regards,
Oskars
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-09 06:00 AM
You’ll need to provide the extended logs for the following: Event, Data, UPS.
Along with a screen shot of the About tab for both UPS / NMC.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-10 04:55 AM
You’ll need to provide the entire logs not just for this time period: Event, Data, UPS
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-19 11:59 PM
The same thing happened to one of other UPS, when Self-Test started, warning that UPS is on battery appeared, so I suppose this is normal that sometimes it appears and sometimes not. This case can be closed, unless there is another explanation.
Link copied. Please paste this link to share this article on your social media post.